gooner35

Just installing some MEM 24way 3ph metalclad DB's and having bit of trouble with rcbo's.
One board has 25 rcbo's along with around 25 mcb's, it's almost done but was wondering if anyone has come across a decent board with room to fit rcbo's a bit easier. Does anyone do a DB with a busbar that eliminates the need for the neutral flylead ?
Also what does that little earth wire do on an rcbo ?
 
Some manufacturer's RCBO's have straight neutral flyleads, eg. ABB, which makes dressing in a lot neater.

The white flylead is a functional earth. In other words for the the functional earth leakage test (user operated test button) to work.
 
nightmare! they dont exist my friend :(

MEM boards are the slimmest so you have even less room if you use those..

my tip...

if you use a Merlin Gerin board.....they make a 2 module wide RCBO ( no taller than mcb but twice as wide ) this picks up the neutal in the busbar with a 'neutral kit' ( very easy to use ..it just clips in ) and eliminates the need for those stupid fat mem flyleads!

we are always expected to cram in too many cables into one DB...fit an additional board if you have too
 
Seems a very expensive job this mate with 25 rcbo,s in 1x board, also if its got 25 rcbo,s in its only a 24way board, is that 8x triple pole ways or 72 single pole ways ?
 
nightmare! they dont exist my friend :(

MEM boards are the slimmest so you have even less room if you use those..

my tip...

if you use a Merlin Gerin board.....they make a 2 module wide RCBO ( no taller than mcb but twice as wide ) this picks up the neutal in the busbar with a 'neutral kit' ( very easy to use ..it just clips in ) and eliminates the need for those stupid fat mem flyleads!

we are always expected to cram in too many cables into one DB...fit an additional board if you have too

As you say Merlin Gerin RCBO's with neutral kit are the way to go but a bit pricey.

Square D dist boards aren't bad except for the curly neutrals but you have plenty of room each side.
 

Reply to 3 Phase DB c/w rcbo's in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K
  • Question
Schneider are best, no doubt...but try pricing (Square D) Loadcentre IKQ, which are now also Schneider. The circuit breakers are exactly the same...
Replies
9
Views
1K
  • Question
I used to make up type A boards using Hager enclosures and devices but Hager will give no warranty on home made boards even with their own...
Replies
8
Views
1K
  • Question
I think you should have started a new thread. Although similar question, the situations are different and answers are now going to be confusing.
Replies
21
Views
11K
  • Question
Ideal. Generally an MCB feeding an RCCB is going to be the most realistic option here.
2 3
Replies
64
Views
11K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks