Some clarification please guys.
Got called out today to wire a 3 phase 32amp Socket into a Builders own 3 phase Genny - (ex AGrreko, bought at auction). Needed to supply a 3 phase plasterers pump system. The genny only had 2x 16amp 240v outlets.
So, opened panel, there was stud terminals L1, L2, L3 & N. Had prewired a board with small CU feeding a socket with 6mm tails coming out. connected these onto the terminals. Turned on pump - nowt.
To cut a long story short, testing with both martindale neon tester & Digital tester showed between 215/220v on all L terminals to N. So far so good. L1/L2 or L2/l3 or L1/L3 all 0V (expected around 415). Coming out of the N terminal was a 10mm earth wire secured to the body of the genny. when I test across this Earth terminal & any L, or for that matter N, then I get 110v which confuses me.
Can somebody explain how this works please?
btw once I worked out that L1/2/3 were the same phase (knackered genny obv) the builder hired a replacement, connected same way to new one and off we went. 10 minutes to do that. 4 hours between connecting original & waiting on replacement.
Got called out today to wire a 3 phase 32amp Socket into a Builders own 3 phase Genny - (ex AGrreko, bought at auction). Needed to supply a 3 phase plasterers pump system. The genny only had 2x 16amp 240v outlets.
So, opened panel, there was stud terminals L1, L2, L3 & N. Had prewired a board with small CU feeding a socket with 6mm tails coming out. connected these onto the terminals. Turned on pump - nowt.
To cut a long story short, testing with both martindale neon tester & Digital tester showed between 215/220v on all L terminals to N. So far so good. L1/L2 or L2/l3 or L1/L3 all 0V (expected around 415). Coming out of the N terminal was a 10mm earth wire secured to the body of the genny. when I test across this Earth terminal & any L, or for that matter N, then I get 110v which confuses me.
Can somebody explain how this works please?
btw once I worked out that L1/2/3 were the same phase (knackered genny obv) the builder hired a replacement, connected same way to new one and off we went. 10 minutes to do that. 4 hours between connecting original & waiting on replacement.