hi all,

a local factory has had a new machine installed which meant their system couldnt handle the load so i installed a generator on the warehouse to run this separatley.

upon monitoring their current usage i noticed phase 2 to always be high, in some case peaked at 80 amps difference between that and the other 2 phases. This obvioulsy creates and imbalance within the 3 phase system and machinery, this results in 'wasted' current. is this difference big enough to cause a lot of potential 'wasted' current? as their supply is only 500amp and they are running close, just trying to delve in to as why they seem to be running so high.

hope this all makes sense!
 
It doesn’t create wasted power. More current will flow in the neutral than necessary. This can some times cause problems where 3½ core supply cables have been used. The calculation for neutral current is N = √ ((A ²+B ²+C ²) - (AxB+AxC+BxC))

If possible look to transferring single-phase feeds from the heavily loaded phase to the others and try to balance the load.

I know it’s an expensive option but an upgrade to the supply would seem in order, but for an 800A supply the DNO would insist on a dedicated transformer.
 
One other thing to look at is power factor corection. If non is fitted the loading could be artificialy high.
 
Last edited by a moderator:
thanks for your reply, sorry yes thats correct causes neutral current. they have been quoted for a new transformer approx £100,000 which taking into account the generator rental costs etc and the fact that a power failiure would cost excessive amounts of downtime its not a great deal money.

i am in the process of explaining about swapping circuits about, unfortuantely the 'engineer' here as wired a room full of single phase boards one the same phase, so trying to get them to run extra phases may not be easy.

thanks for your advice and reply.
 
Obviously you can get a power factor figure from your Electricity bill, online Graphs with usage and peaks.
Check Power factor is correct, and I would be looking at voltage drop on circuits.As mentioned neutral currents and size of conductor important.
 
From what you say the “management” aren’t blind to the problem. Installing the new cables to balance the load is another matter, they will regard it as a small issue compared to the transformer, and to be honest 80A imbalance on a 500KVA transformer is nothing to worry about. 500KVA = 666.7A per phase. BUT once you throw the new machines load on to the system it will rear it’s ugly head again. What is the loading of the new machine?
They will be nailed for exceeding maximum demand on even just one phase. And if as you say the 500A supply is near full load they’ll be sailing close to the wind when the new machine goes on line.
 
Just thinking about it 500KVA just about gets their ar*e out of the fire. 750KVA is more realistic, 1000A gives more room for expansion. But the DNO start getting funny at this kind of loading depending on the location.

One plant I worked on originally had 2 x 250KVA transformers. These were changed to 2 x 500KVA, a few years later changed to 2 x 750KVA. I made brass tags to fit to each transformer pen at this point “Lassie” and “Rover”.
5 years latter “Lassie” and “Rover” were called out of their pens and changed for 1000KVA units, the name tags stuck to their pens!
 

Reply to 3 phase imbalances within system in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
3K
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
663
  • Question
I agree, it is a bit unfair when they change the rules. however, as a nation out usage patterns are changing and the most cost effective tariffs...
Replies
9
Views
2K
  • Question
For anyone looking into the same thing I’ve just found a guy who did an experiment to see if this is how the 3 Phase meters counted units and it...
Replies
3
Views
1K
  • Question
Ok Dave thanks, no more accidents yet 🙏😂….
    • Like
    • Informative
    • Winner
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks