here's one for all you time served electricians out there.......we have a client who has a three phase immersion heater installed in to a bulk tank 1000 litres! that has never been wired up, as he only has a single phase supply, he want us to fit an immerSUN to dump the excess power from his 4kw pv system in to the bulk tank, my question is can it be done?
 
Oh yeah :) Did you not see my three phase system using 3 ImmerSUN's and 4 x 4.5 kW immersions? (2500 Ltr tank though)

The problem you'll have is that they usually share a common neutral, though you can sometimes remove the bridge that connects them, - sharing the common neutral is OK on three phase, but may not be if you are going to wire them up in single phase, as you'll increase the current (depending upon your cable size / the thickness of the bridge)

What rating is the immersion? If like ours it was 4.5kW, you can use two of the elements in parallel to give you 3KW - just remember above re the cable size you'd need for the neutral then. (though it is only 3kW, so not really an issue)[ElectriciansForums.net] 3 phase immersion

The three pahse immersions that we installed actually came with wiring instructions for single and three phase so either 3 x 1.5KW or 1.5kW/3kW/4.5kW.
 
If full load is only 2.5kw just take 240 supply to the immersion link the phases across

That's just what we thought, link across the phases just as the neutrals are already, at 230v 2.6kw comes up at around 11A
just getting a bit frazzled in the sun and needed a second opinion and more ice cream!!!
 

Reply to 3 phase immersion in the Green Lounge (Access Only) area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K
  • Question
I agree, it is a bit unfair when they change the rules. however, as a nation out usage patterns are changing and the most cost effective tariffs...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top