I am installing a 3 phase hose swaging machine, just want to run through the install make sure i have it right, any suggestions welcome. i have been told it will require a 30a 3 phase supply

32A 3phase breaker type c
4mm 3core SWA

From the board, wire to a 32a rotary isolator in 4mm swa, using the armouring as the earth.

From the isolator to a DOL starter,(green on and red off button) in 4mm singles in 20mm plastic copex.

From the DOL starter to the machine, using the lead supplied witht he machine in plastic copex.

Questions...

Does the DOL starter act as a sufficient emergency stop button?
Is it better the wire into a commando outlet so the machine can be changed?
 
The red stop on the DOL starter is only a functional stop and depending on a risk assesment of the machine will establish the need for a E-Stop circuit, if the machine requires E-Stops it would surely be incorperated with-in the machine control system but the fact that you starting machine via DOL starter suggests it dosnt have any control system.
If E-Stop are required then a control panel needs wiring with safety relay and possible 2 channel E-Stop circuit, also when an emergency occurs do all moving parts need to stop instantly or will coasting be acceptable without an inherent risk of injury in the emergency.
To give you an idea about DOL starter been just functional start and stop if you stop the machine using the stop button a failure of the button, a jammed in contactor, incorrectly chosen parts etc all could stop the button stopping the machine which isnt thus classed as fail safe.
If their are inherent dangers in using and working around this machine then the machine requires a control system with limit switches for gaurds and/or removeable panels, because you are wiring the power up a future incident may come back to haunt you as you commisioned the machine by supplying it with power.

The stop button isnt and cant be classed as an E-Stop as it isnt fail safe, a risk assesment of the machine will need to be made as to whether an E-Stop system is required and if so a control panel will be required with a safety relay system doing the Emergency Stop circuit with any limit switch etc incorporated for removeable panels and gaurds where an inherent danger exist.
The DOL starter could jam in, the button could fail electrically or mechanically which means it isnt fail safe or classed as E-Stop, Where as safety relays usually run 2 channels and if anything fails on any channel then the 2 channel will still activate a E-Stop, often more then one contactor is controlled by the relay so jamming or failure of one to release can be covered by a second contactor releasing.
 
Last edited:

Reply to 3 phase install in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

  • Question
Agree with Dave disconnect unused Phases on the outgoing side of the isolator. No reason to replace mcbs with single pole, unless you need room...
Replies
2
Views
1K
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
667
I have sent you my contact details where in the West Midlands are you? I am based north of coventry but travel the county and beyond you may...
Replies
3
Views
971
  • Question
"A catalogue of errors" would be the appropriate phrase here and I agree with Avo and James that HSE need to be involved rather than this forum...
Replies
4
Views
1K
  • Question
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks