3 phase insulation resistance | on ElectriciansForums
Discuss 3 phase insulation resistance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
c.boy
Scotland
WHEN ISOLATING THE D/B TO TEST FOR I/R SHOULD YOU LOCK OFF THE MAIN ISOLATOR AS WELL AS THE MAIN SWITCH IN THE D/B OR ARE YOU OK WITH JUST THE MAIN SWITCH BEING LOCKED OFF?? JUST THINK THAT IF YOU ONLY LOCK OFF THE MAIN SWITCH AT THE D/B THERE IS A CHANCE OF STICKING YOUR PADLOCK KEY INTO THE INCOMERS OUCH!! NOT DONE 3 PHASE TESTING BEFORE SO HOPE THIS MAKES SENSE?? GOT A TEST ON MONDAY JUST WANT TO MAKE SURE!!:confused:
Will you not require the incomers to remain live for eli, pfc test ?
You know you'll be more than careful !! :)
Certainly lock off, and either restrict physical access, or large danger notice and
courdon area out of bounds..
Reply to 3 phase insulation resistance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
If the main switch is on when testing global IR then the neutral and earth will likely give a very low reading. Not that anyone would...
loz2754