sparkie-leeds

Hi All,

The electric board are installing a new 3 phase supply in to the building, they are asking for a 3 phase isolator which is not a problem. From the 3 phase isolator i am running a 4 core 25mm armoured cable with seperate 16mm cpc to a mains board. What i want to know does the 3 phase isolator have to be FUSED, the incoming fuses are 100amp supplied by the elctric board in the main head.

The isolator will be rated at 100 amp aswell.

thanks.
 
If you want to protect the DNO, fuse down to 80amp. Reason.... unlikely damage to swa? Depends on the cable run, I'd say.
 
UK Power in our area only ever ask for a Isolator, if you fit smaller fuses then you are limiting your suppy load so I would say no need to fit fuses, if you still not sure ask your area supplier they will advice what you need m8
 
UK Power in our area only ever ask for a Isolator, if you fit smaller fuses then you are limiting your suppy load so I would say no need to fit fuses, if you still not sure ask your area supplier they will advice what you need m8

I don't feel there is a need to fuse the isolator as its fused at the head, approx. 2 mtrs away from the isolator, just wanted to check.
 

Reply to 3 phase isolator in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
515
This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
721

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top