yep. find the fault. could be contactor coil or several other possibilities.
 
Are you saying that you have a starter and its not latching, so you have to keep your finger on the start button?
If so then do as Tel says and find the fault. You know the motor works so there is something wrong with the latching.
 
Did it work before?
Do you understand basic motor control circuits?

This can be many things as already stated your stop button priority maybe wired wrong and a stop command is active like a limit switch etc .... if its wired wrong its possible to over-ride the stop command by holding the start button in .

Has the motor overload tripped - does resetting it cure the problem? If so you controls are incorrectly wired and you also need to find out why motor O/L has tripped in the first place.

Caution just asking this question gives indication this is not your comfort one and I advice you leave well alone and get someone in who is competent as your lack of experience in this area could endanger others or damage equipment if you try to resolve the issue without understanding both the circuit and risk assessment.
 
Don't you just love these posts.... I'm soooo happy the OP got back to us to give us more info....
 

Reply to 3 phase motor cuts out when button isn't held in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
354
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
905
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I got this all wired in and working thanks to the help from James, absolutely top man. Do have a small issue with current imbalance atm, L3...
Replies
10
Views
2K
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top