at work the other day, a 3 phase motor was running very high amps, when everything checked out we found a loose connection on 1 of the phases back at the DB, cable was melted and burnt. now for me i always thought high resistance would mean less amps would flow, the other electrician put the high amps down to the high resistance. all of the fuses where fine so i dont think the motor was trying to run on 2 phases which i could understand giving high amps.

anyone feel like they could explain this?
 
Last edited by a moderator:
The higher resistance means that you have a greater volt drop over the length of cable.

The motor draws power from the mains so if you transpose P=IV then I=P/V Therefore if you have a higher volt drop then a greater current will flow, usually disipated as heat at the high resistance point; so causing insulation degredation & burning with eventual cable failure.

You would also get slight phasing of the motor due to the imbalanced voltage, causing poor flux density across the affected poles. This will also raise the power required to work the motor compounding the original problem.
 
Last edited:
Hey thanks Notsosmart, thats really cleared that up for me, its all good experience! sometimes you just need to take a step back and have a little think about it or in my case as the question!!!

but yep, thanks again.

Dave:cool:
 
The higher resistance means that you have a greater volt drop over the length of cable.

The motor draws power from the mains so if you transpose P=IV then I=P/V Therefore if you have a higher volt drop then a greater current will flow, usually disipated as heat at the high resistance point; so causing insulation degredation & burning with eventual cable failure.

You would also get slight phasing of the motor due to the imbalanced voltage, causing poor flux density across the affected poles. This will also raise the power required to work the motor compounding the original problem.


I'm sorry but I can't agree your first analysis. Your equation P= IV and its transposition are valid but you forget the equation R=V/I In this case R has increased (contact resistance at the burned terminal) and since V (the mains voltage, not the cable drop part of it) remains at 240v (one phase) so to maintain the equation I falls. Now return to your equation and since V is a constant P drops. ie the power consumed will fall.

But this is not the whole story. Your second analysis is I believe closer to the point. The inballance will cause different current flows in the coils than normal, the motor will slow, and the back emf generated by the motor will fall thereby counteracting the loss of voltage at the motor, allowing more current to flow especially throgh the other two phases. This is known as negative feedback, and it would take me another page or two to fully analyse the reaction of the motor. The overall effect will be an increase in the current in the two good phases and a reduced current in the failing phase.

The fact that the fuses didn't blow simple indiocates that the current was within the rupture current of the fuses.

Now maybe somebody familiar with the design of motors and the effectes of falling back emf will tell me where the flaws are in my arguments.!






The burned out cable it typical of any situation where the contacts have high resistance (bad contact) amd therefore start generating heat.
 
Last edited:

Reply to 3 phase motor, high resistance & high amps. in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

Hi James, At the inverter end the multi strand is ferruled and torqued in the terminal and at the motor end they are the “wago type” push fitting...
Replies
2
Views
306
I got this all wired in and working thanks to the help from James, absolutely top man. Do have a small issue with current imbalance atm, L3...
Replies
10
Views
2K
Hi, Thanks for that, you learn something new almost every day! Regards Griffey
Replies
5
Views
1K
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
3K
As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks