Hi all

Its not often i work with 3 phase so am looking for a bit of advise on cable and circuit breaker size. I have a job to install an isolator for a motor extraction in a small spray booth getting installed in a workshop. I was planning on using 2.5mm single core cable in already installed metal trunking with a 6A type c triple pole circuit breaker. The detail i have on it is
500 BDA
[email protected]
1.5kw motor
2640rpm - 2pole
400w 3 phase 50hz
d90s
FLC 3.0A
SC 21A
 
How did you calculate the mcb size and cable size?
What did the manufacturer say when you asked them what supply they recommend?


Sent from my iPad using Tapatalk
 
Cable size is fine for that load. You could go C16 for OCPD if Zs is satisfactory. That fan will spin up quick so start current will be very short. C6 would be fine. Your data states a starting current of 21A with a running current of 3A.
 
Wot they said. ^^^^
If your ZS is ok the C16 will be ok for short circuit and overload protection of the supply. Then stick an isolator near the motor with a suitably rated DOL which comes combined with an overload device which is suitably rated for the motor.
 

Reply to 3 phase motor in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Hi, Thanks for that, you learn something new almost every day! Regards Griffey
Replies
5
Views
1K
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top