Hi all
Have a 3 phase motor 0.37kw for a small convayor belt, wired up in delta. Does this need a star/delta starter or would it be ok for a DOL starter?
 
hi

if you want to connect it to a d.o.l i would change the windings to star, i imagine if the motor is connected in delta its been used on a single to three phase inverter.
hope this helps

regards
gary.

hawk81 beet me to it
 
Last edited:
Hi
The motor has 9 connections one of them being the earth. May be the extra 2 connectins would be for a variable speed control. which didnt' come with the motor.

Thanks
 
I aggree with all that Gary has said 100%. Many electrician has fallen foul of connecting 400volts accross a 230 volt winding. That could have well been an expensive mistake to have made; it was a good job you had the sense to ask this question on the forum.

Steve..
 
Hi all
Have a 3 phase motor 0.37kw for a small convayor belt, wired up in delta. Does this need a star/delta starter or would it be ok for a DOL starter?


A 0.37Kw motor works out approx Flc 1.2 Amps it would be ok for it to be D.O.L as for wiring it in star or delta it depends on the motor manufacturer. You shouldn't need an inverter unless you want it variable speed
 

Reply to 3 phase motor in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

  • Question
Here are the other drawings
    • Optimistic
    • Funny
Replies
6
Views
1K
Hi All, I have recently purchased a motor soft starter from aliexpress for a 3 phase motor Before connecting load I measured the input and...
Replies
0
Views
566
  • Question
Why are you doing this, you potentially could cause mains transients on smaller power networks and local installations, the reason it has a...
Replies
3
Views
1K
I got this all wired in and working thanks to the help from James, absolutely top man. Do have a small issue with current imbalance atm, L3...
Replies
10
Views
2K
Hi James, At the inverter end the multi strand is ferruled and torqued in the terminal and at the motor end they are the “wago type” push fitting...
Replies
2
Views
306

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks