ive not had a lot to do with motors, what I would like to is if for example a 3 phase motor is quoted as 6kw (forgetting the kva and power factor for a mo) would it normally mean 6kw overall or 6kw per phase ?
Thankyou Lenny for the qick response, I would apprciate if you run your eyes over my calcs to see if I am on the right track, assumming a lagging power factor og 0.85 and 100% efficiency
kva = 6kw/0.85 = 7.05kva
design current Ib = 6000/1.732x400x0.8 = 10.83A per phase
In = say a 3 phase 16A Type D
Cable selection equal or more than 16A per phase
overload protection of the motor would be set within the starter
Reply to 3 phase motors ratings in the Australia area at ElectriciansForums.net
I have sent you my contact details where in the West Midlands are you? I am based north of coventry but travel the county and beyond you may...
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...