Hi, just a quick query about a 3 phase pizza oven folks? The oven is 9 kVA, the run from the board to the isolator is 7 meters swa run in plastic trunking, so I'm calculating;
9 kVA = 9,000 W at near 1 PF (it's an oven so far as I remember it is practically PF 1)
9000 / (root3 X 400) = 12.99
Design current of 12.99 A so therefore a MCB of 16 A
I've not got tables to hand, but I think 4 sq cable should suffice for this.
That sound about right to any of you?