naylorpd
-
Hi, in my garage I have a 3 phase RCCB that has tripped and I just can't get it to reset, even with all the downstream MCBs switched off. Bit of a nuisance really as mother in law has no power to her flat above the garage and the garage door and front gate don't work.
I tried uploading photo but "The uploaded file was not an image as expected." so had to make do with PDF...sorry.
I've tried switching off every MCB that is downstream of the RCCB but even if I can get the RCCB to reset for a minute or so as soon as I switch anything on (just MCBs, not load) it trips again. And once or twice I can reset the RCCB for a minute or so, with no other MCBs on, and it will trip again.
Clearly there is a damp problem in the wall, but actually we are well past winter and ambient temperatures are rising - already around 18-20C. Everything inside the CU looks dry. Cables in the wall are in plastic pipe (UK T&E), except the incoming 3 phase which is SWA, and I guess the 3P link to the upstairs flat is also SWA - can't remember...
Just not sure where to look or what to check. Normally I would turn on the MCBs one at a time until I found which one was causing the trip - but this time it seems to be any of them, or none of them. Actually I've never really had electrical problems here.
I'm in Azerbaijan, I don't have access to a qualified electrician. Apart from design and first fix I did most of the installation myself, about 5 years ago.
Thanks
I tried uploading photo but "The uploaded file was not an image as expected." so had to make do with PDF...sorry.
I've tried switching off every MCB that is downstream of the RCCB but even if I can get the RCCB to reset for a minute or so as soon as I switch anything on (just MCBs, not load) it trips again. And once or twice I can reset the RCCB for a minute or so, with no other MCBs on, and it will trip again.
Clearly there is a damp problem in the wall, but actually we are well past winter and ambient temperatures are rising - already around 18-20C. Everything inside the CU looks dry. Cables in the wall are in plastic pipe (UK T&E), except the incoming 3 phase which is SWA, and I guess the 3P link to the upstairs flat is also SWA - can't remember...
Just not sure where to look or what to check. Normally I would turn on the MCBs one at a time until I found which one was causing the trip - but this time it seems to be any of them, or none of them. Actually I've never really had electrical problems here.
I'm in Azerbaijan, I don't have access to a qualified electrician. Apart from design and first fix I did most of the installation myself, about 5 years ago.
Thanks