eskimo39

Can anyone shed some light on this? I am at a customers house who has a 3 phase supply protected by a main RCD just after the suppliers meter and just before the main consumer unit.

Been having lots of problems with nuciance trips so tested the RCD today with my Megger RCDT320 on a ramp test.

The RCD is rated at 100mA. I connected the gree earth lead and then used the red probe (Phase) to the L1 terminal. The ramp test never tripped the RCD and showed >150mA.

The exact same reading on L2 again with no tripping.

On L3 the RCD tripped but the reading was 140mA.

I am guessing the RCD is faulty but am confused why the customer is still experiencing a lot of nuciance tripping as surely no tripping on L1 & L2 and a very high tripping current on L3 would cause less tripping???

If I install a new 3P RCD which trips correctly on L1,L2 & L3 won't this just trip more??

Another problem that may be connected is I have installed a single phase consumer unit on L3 which feeds gates and exterior lights. I tested the 30mA RCD in this which tripped correctly at 24mA and in .20 seconds. However it also caused the main 3 Phase RCD to trip as well??

Heeeelp
 

Reply to 3 Phase RCD Problems in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
830

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top