Victor

-
Joined
Jun 15, 2008
Messages
212
Reaction score
48
Location
Was France but now Essex
Having fitted a 3 phase RCD at the beginning of the year, I have just been informed by my client that it tripped out during a storm and that when he tried to put it back on, only one of the three phases was operational through the RCD.

I will go back and test, but any in the mean time any advice will be gratefully appreciated.

Thanks in advance
 
check the incomming supply to rcd unit more likely youve lost the phases upstream although its not impossible for the rcd unit to have a fault, it may have taken a surge from a nearby lightning strike, you may need to check the circuits attatched across missing phases just in case the storm tracked down them.
 
It may be wise to check circuits downstream as it may have been a fault current that did the damage even from a lightning strike also is the rcd a front end rccb giving overcurrent protection, if not clamp the power and check it isnt exceeding the rcd amp rating.
 
Could well have been a fault on one of the circuits as well, but all now appear to be ok, just the blown RCD. We are talking old french farmhouse in the middle of the country, very old wiring with mainly no earth connections to either lights or sockets and more extension leads and 3 way adapters than B&Q sell in a year.

I have given him a list of recommendations but it just seems to go over his head that he has a potentially dangerous electrical system. but to top it all the owner says he does not want to pay for a rewire!!!
 

Reply to 3 Phase RCD in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
186
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
570
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
524

Similar threads

  • Question
<= This The RCD looks at any current imbalance between the cables routed though it, if N is not used then no current so it matters not from a...
Replies
4
Views
1K
  • Question
That looks like a Metrel display (I have one), they have a permanent 3 wire display that measures the three combinations so I would say that’s a...
Replies
5
Views
755

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top