Does anyone know what size cable to use for a MCG type 2 SPD (3 phase) and what MCB.the manufacturers instructions don’t state any values!

also should i use 3 x single phase or a 3 phase MCB?
 
If it is anything like this one then 32-63A MCB:
There might be some figured in the new regs on SPD cable sizes but I don't have copies of any with me. I would probably look at 10mm as a typical value to go with.

Generally for good SPD performance you want minimum inductance, so C or D curve MCB if you can get them as well as short cables and cables all close together to keep loop area down.

Some of the smaller ones say 16-32A MCB so maybe 32A D-curve is a choice for all. I would go 3P as if you want to isolate for test you would want all poles off!
 
That’s the exact one but in a metal enclosure, it seems a bit vague on sizes. I will see if i can get 5 x 10mm cables though the bushing, it will be installed touching the top of the 3PH DB with cables just long enough to connect .
thanks for the advice.
 
Just looked at 534.4.10 which has the CPC minimum size as 6mm for type 2, or 16mm for type 1 SPDs.

For the live conductor it has to be rated at prospective fault current (so I guess adiabatic for protection MCB) and also minimum of 6mm for type 1 and 2.5mm for type 2 SPD.

So in your case if you have 6mm cable then probably that will do all and neatly as data sheet shows it is OK.
 

Reply to 3 phase SPD MCB size in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
459
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
It looked like the live connection side ( internally) burned against the neutral of the main switch
2
Replies
23
Views
1K
  • Question
Why not fit a self contained SPD fed directly from the Henley blocks, and free up a bay? Could probably make one up from whats there, using a...
2 3 4
Replies
47
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top