Im pricing to wire an industrial shed. I would like some help in calculating the best rating for the circuit and the cable size.

It has as follows

8 x twin 58w fluorescents - switch or high freq (undecided)? 4A x 90% for diversity =3.6A
3 x 70w metal halides 0.9A x 90% =0.81A
11 x double sockets
1 x 32 2p +e blue socket( this will power a porta kabin)
1 x 1500va 110v tx.
And allow for future expansion

How do i calculated diversity for the 11 x sockets, 32a socket and the tx.

I want to calculate max demand after diversity. And then do the relevant cable calc. Using ((mv/A/m) x ib x L) / 1000


The cable route is 115m long. help with the process would me much appreciated.
 
rough estimate is your load would be around 60A. frfom the info you've given, looks difficult to balance loads between phases. think you should be looking around the 16mm to 25mm for cable size. VD is your main concern as it's a long run.
 
Last edited:
Cheers mate. how would you calculate diversity for the 13a sockets. 32a outside sockets and the tx. I think i did it correctly for the lights. I just want to do it properly to get exact figurefor max demand and then do cable calc. If you wouldnt mind could ylou go throught this process telectrix. Iv got another cable calc job to do so want to do it properly. cheers
 
Cheers mate. how would you calculate diversity for the 13a sockets. 32a outside sockets and the tx. I think i did it correctly for the lights. I just want to do it properly to get exact figurefor max demand and then do cable calc. If you wouldnt mind could ylou go throught this process telectrix. Iv got another cable calc job to do so want to do it properly. cheers
you can't get an exact figure. all depends on the anticipated load. no diversity on the 32A to the porta cabin. say 20A on the 32A socket circuit. you need more info on what loads are likely to be applied and then add on top to cover the worst scenario.
 
Im pricing to wire an industrial shed. I would like some help in calculating the best rating for the circuit and the cable size.

It has as follows

8 x twin 58w fluorescents - switch or high freq (undecided)? 4A x 90% for diversity =3.6A
3 x 70w metal halides 0.9A x 90% =0.81A
11 x double sockets
1 x 32 2p +e blue socket( this will power a porta kabin)
1 x 1500va 110v tx.
And allow for future expansion

How do i calculated diversity for the 11 x sockets, 32a socket and the tx.

I want to calculate max demand after diversity. And then do the relevant cable calc. Using ((mv/A/m) x ib x L) / 1000


The cable route is 115m long. help with the process would me much appreciated.

Any1? please

How quick do you expect answer with a minute between these posts

And then you don't even give us a clue to what the building is being used for let alone what is in the porta cabin plugged into the 32A socket and how many rfc's are to be used for the 11 sockets

In some commercial premises you can be hard pushed to allow much diversity with the duty cycle of the connected load

I would suggest a C&G 2391-20 course would help you and a little patience
 
Theres no need to be like that. I left more than a minute.My browser says a hour. Its just a rush job that iv been asked to quote last minute and I havent got experience in cable calcs. And i wanted to try get a quick verdict incase of any queries. Sorry if it came across inpatient.

The building is being used for storage mainly and some workshop duties. its about 20m x 10m. Overkill on sockets i think but thats what they want. The porta kabin is a small 1 room office, heater few sockets and lights, its on a 32a blue plug.

Yes i would like to go on the 2391-2 course. Im awaiting results on my 2391-10 at the min.

Im keen to see how the max demand is calculated and then from that how the cable calc is done. Many thanks for the help so far
 
you shouldnt be doing this work if you can count in electrix... get hired help and stick to 6A lighting circuits like me, the odd radial and the odd fuse to be replaced,,, this sounds like it could bite you
 
max.demand is very much a hit and miss affair. it's where you have to go with your gut feelings, knowing the client and what he's likely to load the installation with. i'd go a ball park figure of 20-30A per phase, but look at the balance of the 3 phases.
 
max.demand is very much a hit and miss affair. it's where you have to go with your gut feelings, knowing the client and what he's likely to load the installation with. i'd go a ball park figure of 20-30A per phase, but look at the balance of the 3 phases.
but always stick a bit more on top.....just to allow for future proofin....
 

Reply to 3 phase supply cable in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
830

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top