paul-k

Hi I'm having some problems with a 2 phase supply and any help would be appreciated.
I got a breakdown last week on a machine with a 3 phase motor, the contactor was burnt out and the motor windings also. The main contactors and overload have been replaced and the motor rewind completed and tested, but i've got issues with the incomming supply.
On testing each between each phase (red -yellow, red -blue, yellow - blue) i only get 415v on 2 readings indicating a phase down. If i test each individual phase to earth i get 230v so i know i've got voltage on all phases.
The supply cable has been checked and the distribution pannel. I beleive the fault is on the mains supply, but can anyone advise on what it may be?

Thanks,

Paul
 
are two of the phases the same phase? in oher worsd you only get 415v due to each phase being 120o out of sync with eachother. if two of your "phases" are the same phase, then it will register a potential difference to earth of 230v but ther will be no potential difference between 230v to 230v.
 
Where exactly are you testing the supply?

ie. Incoming supply side of main isolator at machine with the switch open (off), at the motor contactor or elsewhere?

.
 
Thanks for replying. I've just been back to site and the fault is on the supply comming from the sub station. The electric company where having problems so they converted the supply 415v to 230v. Hence 230v showing on 3 phases but phases out of sync.
Nice to know they make mistakes too!
 
Checked all the way back to the incomming supply at main isolator. Have now confirmed fault is at the sub station external to the site.
Thanks
 

Reply to 3 phase supply issues in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

Hi James, At the inverter end the multi strand is ferruled and torqued in the terminal and at the motor end they are the “wago type” push fitting...
Replies
2
Views
306
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
3K
I have sent you my contact details where in the West Midlands are you? I am based north of coventry but travel the county and beyond you may...
Replies
3
Views
971
  • Question
Probably a bit late for the OP, but there's a very easy option if a manual solution is OK. Rotary cam switches are just the ticket - but not the...
Replies
4
Views
570
Hi All, I have recently purchased a motor soft starter from aliexpress for a 3 phase motor Before connecting load I measured the input and...
Replies
0
Views
566

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks