Hi I wander if anyone can help?

I have just wired up 2 3 phase motors on a Farm for a Auger System, I have ran in a 3 phase supply from a nearby J.B. There is only 3 phase wires and the outer armour of the cable connected to the body of the box as the earth on the J.B. I have run these into the Control box for the Auger and connected the earths up and the Phaes L1,L2,L3. These are going into the top of the breaker, BENEDIKT JAGER K2-09A. There is connections for the contactor coil A1 and A2, I require a neutral for the coil to work but how do I get this when there is none on the supply I have run??? hmmm I'm stuck:(
 
Cool, can you reccommend any type or part No's for what I require? The Motors are 1.99A x 2 . The type fitted are Benedekt and Jager K2-09A Unit if that means anything?
 
Yes there are pressure sensors and these are connected, one wire is going to the neutral of the coil. God knows how I will find out if these are 400v rated there are no markings?
 
best solutrion is a step down transformer, 415/230v. cheapest and simplest. first try the coil with a 230v supply see if it pulls in.
 

Reply to the thread, titled "3 phase supply no neutral how do i get neutral for the contactor coil??" which is posted in Australia on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Daily, weekly or monthly email

Back
Top