I need to run in a supply for a 3.52kw 3 phase motor 70m from DB i worked out that 1.5 swa in free air would just about be sufficient so thought i would use 2.5mm 4 core
length of Run 70m
P= 3.52kw
v=400
I = P/V = 8.8A
Table 4D4A USING INSTALLATION METHOD E
1.5MM can take 19A
Table 4D4B
voltage drop is 25mV/A/m
length of run is 70m
current is 8.8
total volatage drop would be - 25*70*8.8/1000=15.4
allowed voltage drop
400/100*4=16v
is there some other calculation you do when doing 3 phase - i am not running a nuetral to the motor