M

Maestro

I need to run in a supply for a 3.52kw 3 phase motor 70m from DB i worked out that 1.5 swa in free air would just about be sufficient so thought i would use 2.5mm 4 core

length of Run 70m
P= 3.52kw
v=400
I = P/V = 8.8A

Table 4D4A USING INSTALLATION METHOD E
1.5MM can take 19A

Table 4D4B
voltage drop is 25mV/A/m
length of run is 70m
current is 8.8
total volatage drop would be - 25*70*8.8/1000=15.4
allowed voltage drop
400/100*4=16v

is there some other calculation you do when doing 3 phase - i am not running a nuetral to the motor
 
I'm not doubting your calcs but there's no way I'd install a 70 meter 1.5mm cable to run a 3.5kW inductive (AC3) load.

Is the motor DOL? Is there a VFD or soft starter? Does the motor need to start under high torque conditions?
 
thats why i am using 2.5 - i thought before i worked it out it would be 4 or 6 i even put it into the calculator on Doncastercables and that confirmed 1.5mm, but it is a small motor really it runs a belt driver for fan - its also a Delta wired
 
My 1 question is what is the motor doing is this a high inertia load ... although its a very small motor .... and as already asked what is the starting arrangement of the motor.

Thats 2 questions but just expressing Marvos question as it a good point!
 
Its nice when people get back to you eh....
No mention of fuse/breaker size.
 
OP: Are you sure about this bit:

P= 3.52kw
v=400
I = P/V = 8.8A

Consider: How many phases? What power factor?

Have you checked actual line current given on the motor plate? And as others have mentioned, what is the starting current and permissible voltage drop at that starting current?

is there some other calculation you do when doing 3 phase

Yes!
 
The starting arrangement is Delta - i know i have not added power factor or efficiently rating but i thought if i done it at 100% what would be the big deal the amps on the side of the motor was 7.58A i see know i forget to root 3 the current as its 3 phase but that means i would have got an even lower current so the 1.5 cable size which still seems really small

I just 4mm as there was plenty of that lying around the yard
 
Your missing the point here many factors need to be taken into account - yes you probably have a plated FLC of 7.58amps but this is an highly inductive load also you need to consider your front end device and its ability to handle the starting inrush.

What is your front end device?
What is your method of starting this motor?
What is the starting duty likely to be? (Is this an high inertia load with a long run up time!)
You can't just apply domestic calcs to sizing the cable, you have been asked several questions and not yet answered them so how can we give guidance ?

This is for a belt driven fan and may have an extended starting duty this will create tripping issues if mcb's are used ... is the motor on its own with a starter or is it part of a bigger system and controls.. did you get the ampage directly off the motor plate or the side of a control panel.
 
i will answer best i can i only ever done motors a college and trade test

What is your front end device?
it a belt driven fan
What is your method of starting this motor?
the installer of the fan left DOL Starter with D range Contactor with a thermalover to be conected in it
What is the starting duty likely to be? (Is this an high inertia load with a long run up time!)
i was taking it to be about 10x so was gonna use type C or D MCB
 
i will answer best i can i only ever done motors a college and trade test

What is your front end device?
it a belt driven fan
What is your method of starting this motor?
the installer of the fan left DOL Starter with D range Contactor with a thermalover to be conected in it
What is the starting duty likely to be? (Is this an high inertia load with a long run up time!)
i was taking it to be about 10x so was gonna use type C or D MCB

You need to select you mcb size and type ensuring its large enough to handle the starting curve of the motor usually by referencing the tech' support chart of the manufacturer 'check online' this will give the mcb size required...(its not as simple as type C for motors etc)... once you have a mcb size then select your cable to comply with VD and ELI permitted values .... you may find due to starting duty of the motor you might need a larger mcb to account for this.

The recommended (merlin) mcb for a 3.75kw motor (nearest listed to yours) is a 25amp(b) 25amp (c) or 16amp (d) ... its now up to you to ensure you VD and ELI are met by choosing the correct size cable. Its now showing that your 1.5mm original thought will probably be inadequate .... for the sake of this thread we will omit the OL omit clause for fixed loads as you need to learn to design for motor circuits.

If you are out of your comfort zone here you could do with going on circuit design course or if you feel confident do some web searching and brain cramming ....its an area often messed up and can be costly when it happens.
 

Reply to 3 phase supply to motor cable sizing in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
298
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

Similar threads

Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
997
I have sent you my contact details where in the West Midlands are you? I am based north of coventry but travel the county and beyond you may...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top