I went to some holiday cottages today, the main supply in was 3 phase however only 2 of the phases were used. The L1, L2 and Neutral cables were wired into a three phase meter, then coming out was L1 and Neutral, L2 and Neutral to create two single phase supplies which were divided off using 60amp isolator fuses to each of the cottages with the load roughly balanced over the two phases.

My understanding of 3 phase has only come from large datacenters where although the equipment mainly just used single phase it was always important to try to balance the load over the 3 phases as you got charged based on the peak phase.

Given L3 is not being used does the three phase meter just charge over the 2 phases used or would it be better to have the third phase connected and the load balanced over the three phases.
 
Nope there are about 7 cottages in total plus owners cottage, seemed to be basically 4 cottages on each of the two phases and has been like this for many years.. Each cottage has a 60amp fused isolator in the supply cupboard split using henley blocks from the meter, this then goes to each cottage which each have a consumer unit. No real issue there but was just surprised that given it had a 3 phase meter it only used 2 of the phases, I guess I was expecting all 3 phases to be wired into meter, then from meter into a box to convert to 3 single phases then fed to each cottage, was surprised to see two neutrals coming from the meter.

My main concern was if they were being charged peak phase then obviously having one phase doing nothing means the peak on the other phases would be higher so the bills would be higher. I could be totally wrong.

No plans for any more cottages.
 
I would have thought that it would have been better to have two cottages on each phase and the other (7th) on one of the phases to balance out more.

There are 7 plus owners cottage so 8. But yes I would have thought owners cottage plus largest cottage on one phase and then the other 6 cottages split over the other two phases. There seems to be enough power from the 200amps available for the cottages as no issues ever, all gas heating and no electric showers.

I think it will all be down to how the meter reads the power, if it reads it from power used then does not really make any difference, if it reads it peak power from the 2 phases then better to only have 2 phases as more likely to be a higher difference with 3 phases but if it reads peak power from 3 phases but only using 2 then it would be better to utilise the unused phase.
 
it really doesn't matter a great deal the 3 phase load is not balanced,
it only matters a little if running delta whuch you are not
you are running star configuration.
so if the cables used are correct for the load
then I would not worry at all.
urban myth !
as they say it's a technical nicety not nessicitty.


Thanks, I agree with what you say it was more I was not sure how the meter calculated usage, all other 3 phases I have known get metered on the peak phase rather than actual usage. Thats they only thing that would make a difference.
 
Did you check if it was three phases coming in? Some farms were fed from a split phase transformer. Look and see if the HV line is two wire or three wire. Check the voltage between L1 and L2 around 500v indicates split phase.
 
Did you check if it was three phases coming in? Some farms were fed from a split phase transformer. Look and see if the HV line is two wire or three wire. Check the voltage between L1 and L2 around 500v indicates split phase.

It has 415V warning labels over the cut out... my suspicion is that L1 and L2 are used for the cottages and then next to the cottages is the old farm house that maybe uses L3. I would guess then the meter would be based on Kwh rather than peak phase. The three phase head was completely sealed and I didnt want to take it apart and break the seals.
 
all other 3 phases I have known get metered on the peak phase rather than actual usage

Please correct me if I am wrong but I suspect this to be an oft-repeated myth that has become accepted as fact by many electricians. Ordinary 3-phase meters are just energy meters that register the total energy consumption across all the circuit(s) / phases(s) they are supplying, which is then charged at the prevailing price per kWh at the time it was used according to the tariff. I do not believe that the supplier is permitted to charge for (nor that the meter is permitted to register) energy that was not used.

On large supplies (usually more than your standard 100A 3-phase LV service) the supplier is entitled to vary the tariff according to the nature of the load. So, on a peak demand tariff, if you exceed a certain load for more than a moment, the rate for the billing period changes to a higher price per kWh, on the basis that if your load is peaky it costs them more to generate and transmit. But you still get charged only for the kWh you actually used.

For optimum efficiency of the supply network it is certainly desirable to balance load just as it is desirable to achieve unity power factor and reduce peaks. A few percent of extra unnecessary loss can eat away at the profit margin for the generator and DNO, so their tariffs for large users favour loading patterns that are easiest for them to supply, much like economy 7 for the domestic user. I think it is either this, or badly remembered fragments of theory regarding the 'two wattmeter method' of measuring 3-phase supplies, that have given rise to the belief that a conventional 3-phase meter does something other than just measure total kWh.

True / false??
 
Last edited:

Reply to 3 phase supply to single phases only 2 phases used in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
299
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
282
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
355

Similar threads

Has the cover been removed, is it TP bussbar? I fitted one as @oscar21 linked to a few months ago, it was actually a nice board and with the TP...
Replies
5
Views
534
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
926

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

  • exceeding voltage drop
    The cable is way undersized. If the voltage drop is detrimental to the installation I would make...
  • TT advise
    OK My take on the precautions to implement when omitting an up front RCD on a TT system. Tails...
  • SIL vs ATEX
    Good morning all, I have a question for those who are CompEx and SIL aware - I have various Ex...
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top