Hi all..
Bit of a nightmare afternoon,, testing a caravan park TP&N panel board IR testing while board isolated before returning power (merlin gerin panel board) over the next 30 mins customers on park are reporting loud bangs inside some of there vans, boilers and electric fireplaces (with pcbs) exploding..
Wondering if any1 else experienced similar or shed some light on this..
Seems to me like it could be a temporary loss on Neutral somewhere be it a downstream fault in cable, loose neutral or dodgy main switch (was 4 pole) if the neutral lost on 3 phase with then single phase circuit voltage rising to 400v+ would have caused this pcb problems..
Appreciate and info