I was just wondering if anyone would be able to help me with my question I have, it's about testing a 3 phase motor that has a contractor and overload, like I know that continuity and insulation resistance you would link out the contactor and overload but for the live tests I can't seem to see how you go about it? Like for a zs test? If there isn't a neutral at the socket for the motor how can you do a 3 lead test for zs and pfc? Thanks in advance if you can help, just an apprentice btw
 
If your doing a Zs test you are effectively looking at the earth fault path(L-E) so N isn't needed, if your meter doesn't have a 2 wire option then connect N clip to earth as the meter is only using it as a ref' that you have a supply and isn't needed for the testing itself.
Test each phase to earth separately and note the worse reading.
 
Last edited by a moderator:
So when you're doing what you're saying have you linked out the contactor and overload or just pushed the contactor in? To close the circuit? I was thinking, see how zs=ze+(r1+r2)
could you use the r1+r2 given by the meter and the ze from the meter reading
 
R1+r2, you can get a meter value for that by linking out the contractor and overload (so it closes the circuit) and test from there, using the r1+r2 you get you could then add that on to the ze of the board it is feed from? No? So for example say you're r1+r2 for the motor circuit is 0.85 and Ze = 0.35, could you not using Zs=ze+(r1+r2) say 0.85+0.35 = 1.20 therefore the zs of the motor is 1.2 ohms?
 
3 wire efli tests are intended for use only when it is impossible to use a proper high current test. So unless your motor is on an rcd you should be using a 2 wire high current efli test
 
Hi dude,your original question referred to the testing of a three phase motor...i presume you mean the fixed wiring testing,and not any tests performed on the actual motor.
 

Reply to 3 phase testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
508
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
979
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
909

Similar threads

Think all has been covered already, but echo-ing the above if I was getting my DB swapped and had a 3 phase head, I would put a little TPN board...
Replies
5
Views
495
  • Question
I believe that it is incorporated into the 5 days. But will double check. Thanks.
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top