Hi all, done a lot of single phase testing but not much on 3 phase.any advice on this part of testing like loop readings when testing ie between phases and psc values, any advice greatly appreciated folks:smilewinkgrin:
 
Good question mickytuff, this part of the site i think is great for learning. I hope you get some usefull tips on this. I'm gonna let someone else start the bun fight but for now just get to know all the functions on your meter as it will make the answers you get easier to understand.
 
For PSCC test between Phase and neutral, then double it. And for the Ze do Each phase to Earth and take the highest reading..
 
they teach you to double your phase to earth/neutral, but its actually closer to x 1.732.
if your tester requires a neutral for Zs, and you have a balanced 3 wire load, then you can put your neutral lead on the CPC.
 
they teach you to double your phase to earth/neutral, but its actually closer to x 1.732.
if your tester requires a neutral for Zs, and you have a balanced 3 wire load, then you can put your neutral lead on the CPC.

We are taught to double it because it is easier for the maths and memory, and err's on the side of caution. It also an acceptable answer if the question crops up on the 2391 course. There are Instruments about which can do phase to phase, but unless you know for certain then assume it wont and do the calculation, cos if you do and it isnt, you wont like it, and neither will the instrument.

Cheers........Howard
 
other things relevant to 3ph testing, is on R1 + R2, and Zs, it is the highest of the three phases that is recorded. As part of the functional tests, phase rotation must be tested.
During inspections, one of the extra items that must be checked, such as that all phases and neutral pass thorugh the same hole in ferrous containment, unless a slot is cut between seperate holes.
balncing of loads is also another consideration, although in practice its almost impossible to do perfectly.
 

Reply to 3 phase testing??? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
309
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
832
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
930

Similar threads

Given that a lot of EV's only charge from one phase when connected to a 3 phase chargepoint does the customer really need a 3 phase chargepoint...
Replies
1
Views
604
All of the information for MG stuff is freely available from Schneider
Replies
8
Views
765
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top