Hi all, done a lot of single phase testing but not much on 3 phase.any advice on this part of testing like loop readings when testing ie between phases and psc values, any advice greatly appreciated folks:smilewinkgrin:
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss 3 phase testing??? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
they teach you to double your phase to earth/neutral, but its actually closer to x 1.732.
if your tester requires a neutral for Zs, and you have a balanced 3 wire load, then you can put your neutral lead on the CPC.
... phase rotation must be tested. ...