Hi all,

This is a great forum, a big thank you to all those that made it possible,

I hope you good people can help me:

I have a 3 phase 10HP pump that I would like to turn on/off with a timer switch over a weekly program,

looking online I can not find much other than some Chinese device,

one idea was suggested to me was to use a contactor with a coil and timer switch that will act on the coil
to turn it on/off?

can someone please suggest an easier simpler cheaper way of achieving my aims - perhaps with links as to where I can buy the required kit?

Many thanks
 
Wot 'e sed!^^^^^
Having been involved in heating system controls for nearly 40 years, the standard way is a 3 or 4 pole contactor with a 230v coil controlled by whatever timer that you fancy/suits your needs.
 
As above, some standard timer and a contactor.

10HP is a fair bit of motor to switch. Depending on the starter (star-delta or DOL) you might be needing a contactor rated at 63A or so to meet the switch-on surge. Check the contactor data sheet as they typically give several switching limits with the headline being the most favourable for a simple resistive load (e.g. heater).
 
You'll need a contactor with an IEC AC-3 rating comfortably over 16A (AC-3 loads include squirrel cage motors) or an IEC power rating of 7.5kW or more. These rating take into account the starting current of the motor and are lower than the thermal or AC-1 rating of the contactor, so they don't need to be inflated. Most timers have a limit of 250V on their output contacts so the coil will need to be 230V. This assumes your supply has a neutral - some motor circuits don't if the existing switchgear doesn't require one. Confirm that before you start ordering!

But...
What switchgear / starter is in use at the moment? Is it D-O-L? Could the timer be connected into that? If the existing starter has NVR, you need to consider the effect of adding an outboard contactor.
 
Last edited:

Reply to 3 Phase timer switch in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
951
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Yet another update: I believe what EDF have done is moved me from an Economy 9 to an Economy 7. I've just emailed them to ask if they can switch...
Replies
2
Views
267
  • Question
Probably a bit late for the OP, but there's a very easy option if a manual solution is OK. Rotary cam switches are just the ticket - but not the...
Replies
4
Views
694

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top