A

anthanth

(sorry this went into a few forums it should not have -my bad)

Any help would be great

A volt drop calculation that i could do with some help with is the 3 phase VD


I fully understand the single phase vd calculations but just wanted to get a confirmation when using 3 phase.

e.g

Say a large load of 30Kw is 200m from the point of distribution and you need to find out the volt dropped.

Do you use 30000/230 - 130 Amps or

do you use 30000/415 - 72 Amps????


Now lets say using a 50mm conductor the differences are below.

230 ---- 0.84 x 130 X 200 (m) /1000 = 21.84 volts dropped
415 ---- 0.84 x 72 x 200 (m) /1000 = 12.0 volts dropped

At 415 v this would be approx 3% vd!!

Have a got this correct or would some body like to correct me?

Just looking for some help................

many thanks
 
3 phase calcs are different to single phase calcs.

Without my books with me, ill try and remember the calcs.(im sure if im wrong, someone will shoot me down)

Design Current Ib = 30000/400*1.732 = 43.30amps (Cos phi, efficency e.t.c assumed to be 1)

You say a 50mm conductor, is this swa, singles, multicore SWA???? ill assume 0.84 is correct for now

so @400v 0.84*43.30*200/1000 = 7.27volts.

Your allowed 3% VD for lighting circuits so 12v in a 400v system
Your allowed 5% VD for other loads so 20v in a 400v system.
 
now i do it a simpler way. as long as the load is balanced...... 30kw is 10kw per phase, so 43.48A per phase. then as above..

(43.48 x 0.84 x 200)/1000
 
Hi there, thanks for the updates. Ok it is a SWA cable in the ground.

I understand the workings above but would like to check why i came out with 72 amps and
you came out with 43.48.

It seems to do with the 1.732 that i missed. (30000 / 400 X 1.732) instead of my 30000/400

Can you let me know where this came from and why is it used??


Thanks again for the info

getting there................
 
Ah ha ok. Many thanks for the input above. Just to clarify for my own sake with an example......

say there is a 70 Kw load and it is fed from a supply 400m away, if you were to use a 50mm swa cable then is the below calculation correct??


70000/400 * 1.732 = 101 Amps (per conductor - correct?
so

0.84 X 101 X 400/ 1000

= 33.9 volts dropped


(i used 0.84 from table 6D2 in OSG however the table 4J4B in the regs gives very different firgures, which i assume to be to do with reactive and resistive factors)

So do i have the above correct. Obviously the volt drop would to too high for lighting and normal loads so a larger cable would be needed but the calculation was all that i was after.


Thanks to all for input thus far.......
 
ah ha ok yes i was using the wrong tables using the 4E4A it is slightly different (SWA table)

50m cable, 70 kw load, 400m

0.86 X 101 X 400 / 1000 = 34.7 V

Oui or non?
 
it looks good, although you do realise you are using the table for 90`c cable... only use this cable if you comply with the 2 notes written next to the table.

As far as the calcs go, looks fine to me from a basic point of view.

Good link from Lenny above.
 
In truth the fact is ..... it's still 415V/240v, ...the 400V/230V is just an imaginary voltage to please the harmonisation crap we've been saddled with....
 
Duplications deleted.

Common industrial voltages in use in the UK, all 3ph are 400V, 415V, 440V, 460V and 480V. Go to Norway and they insist on using 690V if an installation is above a certain size also.

Probably a tutorial question that was posed back when 415/240V was the norm.
 
Last edited:

Reply to 3 phase volt drop in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

  • Question
Thanks for the replies, that's given me a bit to think about! :-)
Replies
6
Views
2K
Surely that will depend on what is connected to it. And the nominal voltage between phases is 400V (+10%/-6%).
Replies
3
Views
851
  • Question
Because the VD values given in the related column are for that case. The alternative is to consider 3 pairs of single phase cables, for which you...
Replies
5
Views
2K
  • Question
Just to add that generally speaking I don't like spurs off RFC as they break the excellent end-end test that all CPCs are connected, etc. However...
Replies
2
Views
2K
  • Question
I think technically it is the 400V that is "rounded" as the ESQCR actually gives the nominal value UK LV supply as 230V L-E here...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks