Chaps,
New to the forum with an opening queery as follows:
I am required to install a 3phase PSU. PSU is essentially a bunch of rectifiers to power DC coms equipment. Clients design is for a 40A 1pole type C MCB x3. I suggested that a Type D 3pole is more suitable and that as best I know it 3x 1 pole MCB's would be contray to BS7671. Client asked why and my reply was that in the occurence of a fault on 1 phase all 3 should be disconnected for safety reasons. NICEIC were inclined to disagree and said that it was acceptable as it would cause safety only if a motor was liable to stop a piece of equipment and that for the equipment in question it would be ok. Pondering the matter further I thought, how can it be safe if someone who assumes the kit is dead, as they only test on the de-energized phase during safe isolation, plays around with it while 2 phases are still live?
New to the forum with an opening queery as follows:
I am required to install a 3phase PSU. PSU is essentially a bunch of rectifiers to power DC coms equipment. Clients design is for a 40A 1pole type C MCB x3. I suggested that a Type D 3pole is more suitable and that as best I know it 3x 1 pole MCB's would be contray to BS7671. Client asked why and my reply was that in the occurence of a fault on 1 phase all 3 should be disconnected for safety reasons. NICEIC were inclined to disagree and said that it was acceptable as it would cause safety only if a motor was liable to stop a piece of equipment and that for the equipment in question it would be ok. Pondering the matter further I thought, how can it be safe if someone who assumes the kit is dead, as they only test on the de-energized phase during safe isolation, plays around with it while 2 phases are still live?