Can someone remind me
Is a type 2 breaker = to a type B
Can't find my file
Many Thanks
 
Lenny
That would possibly explain the problem- are the starting characteristics similar eg Type B, 3 times, C, 7to 10 times
Been to look at an old control panel. 3 of the type 2 rated 25amp breakers were defective (very unusual!)
Been informed a "sparky" was holding then in whilst starting the motors.
My line of attack- obtain Flc of motors- check cables and sizes- and rate and size breakers for type C (motor rated with infrequent starts- if many starts type D)
 
A type D breaker should not be fitted with a motor, only fit a type C. The overloadand contactor fitted on the motor should only do 6 starts an hour, if more starts are reqired fit an inverter. more expensive but its the right way
 
Why do Merlin Gerin and every other manufacturer give a table in their catalogues for motor starters
showing the recommended MCB IN TYPE H, TYPE C & TYPE D
eg
4kW 5.5HP 3 phase c 20amp d 16amp
Are you saying the manufacturers are wrong or do you have a reason. Is it to do with the let through energy, in that case you have to size the contactors to suit.Or
Is it the type of co-ordination (where things are allowed to be damaged to a certain degree ) under a fault condion.
The parts then have to be replaced
 

Reply to 3 pole minature circuit breakers in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
155
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
522
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
465

Similar threads

  • Question
A 2 pole breaker will have a bar between the 2 breakers and the slim line breakers that you are referring to are just 2-15 or 20 amp single pole...
Replies
1
Views
547
Noted. Thank you. Out of phase summation being the answer to the question.
Replies
14
Views
916

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top