Having been one of the culprits who wired 2.5 ring mains with 1.0mm cpc in times past
I am going to do some repositioning of sockets in a kitchen which is being extended
It has rewireable fuses pre-dating the standard wylex rewireables

Before taking on the work I tested the existing ring and looked in the good book for max zs because there is no chance whatsoever of rewiring for various reasons
Having in the past seen and used 30 amp fuses for these on numerous occasions,I was surprised they appear to be not listed in the on site guide
The way I am reading it,30 amp fuses on a 1.0mm cpc ring are not permitted
(Having said that working my way through guide books has never been a strong point with me)

Is this correct or am I cocking up somewhere?
The only reason I can come up with is possible thermal effects on the 1.0mm cpc

Your advise and/or knowlege would be greatly appreciated
 
Des 3o fuses and 32a mcb,bs88 (with rcd protection) is ok.

With rings it is esentially a duel supply to each point so its 5mm and 2mm cpc.
As its a ring what is assumend on a perfect situation is 16a load per leg to md pot so your "2.5d 1mm cpc is allowed. If in dought try the adiobatic to prove ring size section its arround section 520530 of BRB
 
Table 41.2 of the brg, max Zs for a 30 amp fuse to BS 3036 1.09 ohms.
Appendix 15 conductor size of ring, live=2.5mm, cpc=1.5mm

However, 433.1.3 say where the protective device is BS3036, you must de-rate the current carrying capacity of the cable by 0.727.

So, add this to the need for rcd protection, you should change the protective device to an rcbo or better still fit a new consummer unit.

As to wether you can extend a final ring circuit that has a 1mm cpc rather than rewire the whole circuit.................

I dont know!
 
Thanks for the reply scotsparky
I have done the adiabatic and its ok
What was throwing me was the statement at the bottom
The combination of the protective conductor and the fuse is not permitted


If I assume equal load down both legs and 2x1.0mm cpc then the statement does not apply?

Table 41.2 of the brg, max Zs for a 30 amp fuse to BS 3036 1.09 ohms.
Appendix 15 conductor size of ring, live=2.5mm, cpc=1.5mm

However, 433.1.3 say where the protective device is BS3036, you must de-rate the current carrying capacity of the cable by 0.727.

So, add this to the need for rcd protection, you should change the protective device to an rcbo or better still fit a new consummer unit.

As to wether you can extend a final ring circuit that has a 1mm cpc rather than rewire the whole circuit.................

I dont know!


There is an existing 30 m/amp rcd and the main earth conductor and protective bonding are to standard
The lenghth of circuit will not be extended as such
I have suggested a new consumer unit,but the soon to be kitchen fitter has already agreed with the householder to fit one later on(thats one reason why I am checking the compliance before commencing the work, I may have reason to quote for the consumer unit before him (defined scope or not he is taking work off me,maybe work he should not be doing )
I will be working for a builder and will do whats required for him,but my install/alteration needs to be correct ,new consumer or not,but the guide threw a panner at my understanding
Thanks for the replies
 
Last edited:

Reply to 30 amp rewireable fuse + 1.0mm cpc in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
834

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top