Hi there
if anyone is able to show me how to go about working out this question it would be most appreciated.
I think that it will require haveing to look at either the on site guide bs7671:2008 or the IEE wiring regulations seventeenth edition thats the only thing.
A pvc trunking is used to enclose single core PVC insulated distribution cables (copper conductors) for a supply to a new 400 V TP&N distribution board. The balanced load consists of a 24 KW of discharge lighting. The fuses at the main switchboard are to BS88. The voltage drop must not exceed 6V. The ambient temperature is anticipated to be 35 oC. The declared value of IP is 20 KA and the ze is 0.3 ohms. Assume that the requirements of BS 7671 434 are satisfied by the use of BS88 fuses. For the distribution cable determine the
i. design current
ii. the maximum rateing of the fuse in the main swith fuse In
iii. maximum mV/A/m value
iv. minimum current rateing It
v. minimum cross sectional area of live conductors
vi. actual voltage drop int he cables
Ive had ago at finding the design current and the rateing of the fuse (In) which I think is a s follows
Ib = 24000/400x1 = 60 Amps
In = greater then or equal to Ib = 63 amps
but then I get stuck
if anyone is able to show me how to go about working out this question it would be most appreciated.
I think that it will require haveing to look at either the on site guide bs7671:2008 or the IEE wiring regulations seventeenth edition thats the only thing.
A pvc trunking is used to enclose single core PVC insulated distribution cables (copper conductors) for a supply to a new 400 V TP&N distribution board. The balanced load consists of a 24 KW of discharge lighting. The fuses at the main switchboard are to BS88. The voltage drop must not exceed 6V. The ambient temperature is anticipated to be 35 oC. The declared value of IP is 20 KA and the ze is 0.3 ohms. Assume that the requirements of BS 7671 434 are satisfied by the use of BS88 fuses. For the distribution cable determine the
i. design current
ii. the maximum rateing of the fuse in the main swith fuse In
iii. maximum mV/A/m value
iv. minimum current rateing It
v. minimum cross sectional area of live conductors
vi. actual voltage drop int he cables
Ive had ago at finding the design current and the rateing of the fuse (In) which I think is a s follows
Ib = 24000/400x1 = 60 Amps
In = greater then or equal to Ib = 63 amps
but then I get stuck