I assume you mean BS3781 cartridge fuses and MCBs NOT BS3036 semi-enclosed rewirable fuses.
Time curves for BS 3871 devices
The time/current curves for BS3871 MCB's you're looking for are in 16th edition of the wiring regulations BS7671:1992 AMT 2, BYB, or earlier.
Time/Current Characteristics:
BS3781 40A Type 1 MCB, 0.1 to 5s = 160A
BS3781 40A Type 2 MCB, 0.1 to 5s = 280A
BS3781 50A Type 1 MCB, 0.1 to 5s = 200A
BS3781 50A Type 2 MCB, 0.1 to 5s = 350A
The older style MCBs were BS 3871, and were numbered Type 1, 2, 3 and 4.
The characteristics for the old type are similar but not the same as for the new BS EN 60898 versions.
Type 1: 2.7 - 4 In, Type B: 3 - 5 In.
Type 2: 4 - 7 In, Type C: 5 - 10 In.
Type 3: 7 - 10 In, Type D: 10 - 20 In.
Type 4: 10 - 50 In.
During the change over of the standards, manufacturers were allowed to use the new BS EN 60898 designations on the old BS3871 devices, if they were within the limits specified.
For instance a Type 1 is within the specifications for Type B.
Types 2 and 3 are within the specifications for Type C.
However Type 4 is outside of the specifications for Type D.
The value of Zs in BS7671:1992 AMT 2, are at a nominal voltage 230V as required in later versions. However, be careful when using the Zs values from old versions of BS7671, the nominal voltage will be 240V. The voltage is relevant because the current required to disconnect in the correct time divided into the voltage gives the ZS max values for the CPD. A nominal voltage of 240V will therefore result in a proportional higher Zs max, than now allowed. If you have the old Zs values divide them by 240 then multiply by 230 to get the new values.