Hi there, i was wondering if anyone could help me out quickly, BS3036 fuses that still use the original carrier but have been replaced with plug in mcbs....any idea on the BS number of these? Cant find em in the regs book and trying to find max Zs...? Cheers
 
This type is as Hifly suggested a standard B Curve 60898
[ElectriciansForums.net] 3036 mcbs
 
Last edited:
I assume you mean BS3781 cartridge fuses and MCBs NOT BS3036 semi-enclosed rewirable fuses.

Time curves for BS 3871 devices
The time/current curves for BS3871 MCB's you're looking for are in 16th edition of the wiring regulations BS7671:1992 AMT 2, BYB, or earlier.
Time/Current Characteristics:
BS3781 40A Type 1 MCB, 0.1 to 5s = 160A
BS3781 40A Type 2 MCB, 0.1 to 5s = 280A
BS3781 50A Type 1 MCB, 0.1 to 5s = 200A
BS3781 50A Type 2 MCB, 0.1 to 5s = 350A

The older style MCBs were BS 3871, and were numbered Type 1, 2, 3 and 4.
The characteristics for the old type are similar but not the same as for the new BS EN 60898 versions.
Type 1: 2.7 - 4 In, Type B: 3 - 5 In.
Type 2: 4 - 7 In, Type C: 5 - 10 In.
Type 3: 7 - 10 In, Type D: 10 - 20 In.
Type 4: 10 - 50 In.

During the change over of the standards, manufacturers were allowed to use the new BS EN 60898 designations on the old BS3871 devices, if they were within the limits specified.
For instance a Type 1 is within the specifications for Type B.
Types 2 and 3 are within the specifications for Type C.
However Type 4 is outside of the specifications for Type D.

The value of Zs in BS7671:1992 AMT 2, are at a nominal voltage 230V as required in later versions. However, be careful when using the Zs values from old versions of BS7671, the nominal voltage will be 240V. The voltage is relevant because the current required to disconnect in the correct time divided into the voltage gives the ZS max values for the CPD. A nominal voltage of 240V will therefore result in a proportional higher Zs max, than now allowed. If you have the old Zs values divide them by 240 then multiply by 230 to get the new values.
 
Last edited by a moderator:

Reply to 3036 mcbs in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
897

Similar threads

  • Question
My thoughts exactly! Snowed under with work at the moment, so might have to pass it on 😬😬
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top