Joined
Jan 21, 2011
Messages
581
Reaction score
34
have a customer with a 3036 rewireable board. i Need to provide rcd protection for 1x30a ring circuit and 1x5a lighting circuit for additions. my plan is to remove the ring main and lighting circuit from existing fuse board.

From one of the now spare ways run a 6mm2 t+e fused at 40a to a new 2way 63a 30ma C.U. the ring main now on 32a mcb and lighting 6a mcb both circuits now rcd protected.

anyone see any issues ??
 
is not replacing the D.B. a better option? for a few quid more than you are already spending on the additional 2way board complete you could get a full 17th edition board, im sure a chat with your customer is what you need to do, spend now save later and flexibility to expand.
 
just done a quick cable calc re correction factor for a 3036 fuse.

6mm2 rated current 45Amps 45x0.725 = 32.625 (In Max)
10mm2 rated current 65Amps 65x0,725 = 47.125 (In Max)

it = in/Cc 40/0.725 = 55.17

ib=38<In=40<Iz=65

so my original plan to use 6mm no good will have to be 10mm feed to 2nd cu.
 
Last edited:
apart from a new dual rcd main C.U any other options for providing rcd protection to both circuits.

just thought only one lighting circuit/ ringmain my oriiginal plan would put both on single rcd which i want to avoid. Im hoping they will opt for a complete new main cu.
 
Last edited:
1mm more than likely cannot take the fault current to operate the OCPD in the required time.
If it is 1.5 there is the option of fitting a rcd after the consumer unit, in a 2w enclosure for each cct.
Although i personally think your options are the way to go :)
 
Connect the new circuits into a small enclosure containing 2 RCBO's for lights / sockets.
Feed this unit with 6mm T&E using one of the spare fuseways fitted with a wylex
plug-in 40A mcb , saves having to derate due to rewirable :)
 

Reply to 3036 rewirable rcd protection in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
752

Similar threads

  • Question
even allowing for diversity this sounds a bit tight for a 100 amp supply, can you tell us what the existing circuits actually have connected to...
Replies
2
Views
710
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
945

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top