309 written exam. Neutral current in an unbalanced 3 phase system. | on ElectriciansForums

Discuss 309 written exam. Neutral current in an unbalanced 3 phase system. in the Electrical Course Trainees Only area at ElectriciansForums.net

Simonslimline

-
Arms
Joined
Jan 13, 2013
Messages
2,195
Reaction score
1,081
Location
South West, Bath
Had the 309 science and principles exam today at college and had a question on calculating the neutral current flow in a 3 phase 4 wire system with unbalanced loads. The formula is below, and definitely one to memorise.

N=√((A²+B²+C²)-((A×B)+(A×C)+(B×C)))

:)


 
Last edited:
Cheers for that :) Nice handy formula. Will probably stick to:

x = A cos 0 + B cos 120 + C cos 240 (or, x = A - 0.5B - 0.5C)
y = A sin 0 + B sin 120 + C sin 240 (or, y = √0.75B - √0.75C)
N = √(x²+y²)

... as I can picture in me head where it comes from.

You way's neater, though! :)

Got 2365 302 (which I think is pretty much the same as 2357 309?) in a few weeks' time. It's been a looooong unit....
 
Had the 309 science and principles exam today at college and had a question on calculating the neutral current flow in a 3 phase 4 wire system with unbalanced loads. The formula is below, and definitely one to memorise.

N=√(A²+B²+C²) - (A×B+A×C+B×C)

:)



You need a few more sets of brackets in that formula to make it work.

N=√((A²+B²+C²)-(A×B)+(A×C)+(B×C)))

Try working it out both ways with made up values and you'll see what I mean.
 
You need a few more sets of brackets in that formula to make it work.

N=√((A²+B²+C²)-(A×B)+(A×C)+(B×C))

Try working it out both ways with made up values and you'll see what I mean.

One more set of brackets for ya:

N=√((A²+B²+C²)-((A×B)+(A×C)+(B×C)))

... otherwise you end up adding the (AxC) and the (BxC); they need to be subtracted from the squared terms just like the (AxB).

Between us, we'll get there eventually! :)
 
Yes Steve that's correct was still sleeping when I put the brackets in lol. Going to edit now as per my notes.
In=√((Ia²+Ib²+Ic²)-((Ia*Ib)+(Ia*Ic)+(Ib*Ic)))
 
Applying this formula to the neutral current calculations from my AC theory class today suggests that it only applies on resistive loads, have you covered reactive loads and vector addition yet Simonslimline? Happysteve's variant could be made to work, but only if you changed the Sin/Cos 120/240 to the correct phase angle of the load.
 
I took the formula from the thread below a while back. I am going to do some reading about what you have posted, Nice 1 :smile:



http://www.electriciansforums.co.uk/commercial-industrial-electrical/39855-electrical-theory.html




Applying this formula to the neutral current calculations from my AC theory class today suggests that it only applies on resistive loads, have you covered reactive loads and vector addition yet Simonslimline? Happysteve's variant could be made to work, but only if you changed the Sin/Cos 120/240 to the correct phase angle of the load.
 
i got a question about the neutral current in my 309 exam 2 weeks ago but we wasn't allowed to do it mathematically it asked us to do it graphically so we had to draw the vector diagram and that but i thought it was a easy question really haha
 
simple way we have been taught, dont know how to put math symbols up so ill do my best.

3 phase and neutral, Ph1 50, Ph2 40, Ph3 10 and N ?

Take the smallest number away from the other numbers, so 50-10 and 40-10, gives you 40 and 30 respectively.

N= square root of 40 squared-30 squared so N= square root of 1600-900 so N= square root of 700 so N=26.5

sorry about how its written out, hope you can follow it
 
N=√((A²+B²+C²)-((A×B)+(A×C)+(B×C)))

yep, i get 36 when i do it that way aswell!........i never thought to check against what the tutor told us.

bit ****ed off, i have my 309 written exam on tuesday and no more classes to clarify this.

cheers
 

Reply to 309 written exam. Neutral current in an unbalanced 3 phase system. in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
354
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
905
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top