Can anyone help the drawing shows a split phase supply
feeding 2 biuildings whith a fire alarm serving the 2
the alarm panel is supplied from building 1. And runs underground to building 2
some detectors are mounted on steel and therefor bonding the 2 together when ther is a load of
60a in biuliding 2 up to 30a can be seen in the earth
i have now put a 35mm earth between the buildings the current is now flowing through this.
Instead of the fp200
wpd have been out and can find no fault
  • [ElectriciansForums.net] 30a. In earth bond
Reply to 30a. In earth bond in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...