tomchester999

Hello all!

I am working in a property with 3 old rewirable fuseboards, each fed from mcb's in a modern consumer unit at the incoming supply.

We want to change the 3 fuseboards to 17th ed RCD etc. However, as the 16mm T+E is less than 50mm in the wall I wonder whether I should protect each submain at the source with 30ma RCD or RCBO or just leave it as it is (currently 100ma at source)

Obviosly if it were to trip 2 floors down it would be really annoying, but do I need the protect the 16mm in the wall? Running new supplies in armoured is out of the question unfortunately..


thanks in advance for any advice!
 
did a similar job in some flats. RCBO for each 16mm fitted in main CU. 2 years on and no tripping problems. in this case, though, the landlord lives on site, so not a problem to reset. also, it saves fitting RCD protection in each sub-main.
 
I would be seriously tempted to protect with 30ma at the source purely to protect the 16mm t&e. It may as you say be a nuisance should it trip at the source but better that than the alternative
 

Reply to 30ma for existing 16mm T+E submain ?? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
850

Similar threads

  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
827
As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
267

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top