Hi all
Ok...been to a job today with a random tripping 30mA rcd
its a bit of a full on install...at a undertakers....
3p cutout feeds 3 main switches...1 for a workshop db...for a flat over the undertakers...1 for the undertakers....
from the undertakers mainswitch...we have a swa submain to a db...3 more submains to 3 other dbs..one of which goes to a small garageon the se o the flat.
customer says that when he swtches on flouresent lights (any..connected to any of his 4 db's) sometimes his rcd trips..
ive seen this today...
so...ramp test the rcd...(hager 100A 30mA .....fitted it 18 months ago when the last one tripped to early..!) goes off at 17mA every time.
when I switch off the submain to garage .... it goes out at 23ma..and all is fine.
sub main tests fine...
submain db tests fine..all its cabling tests fine....
turn off submain db circuits one at a time...no difference...still trips at 17mA.......
ill return to the job as I ran out of time.....
ANY THOUGHTS....?? GREATFULY ACCEPTED
can it be just a mass of leaky appliances all contributing...???
let me know..
cheers
vitoboy
Ok...been to a job today with a random tripping 30mA rcd
its a bit of a full on install...at a undertakers....
3p cutout feeds 3 main switches...1 for a workshop db...for a flat over the undertakers...1 for the undertakers....
from the undertakers mainswitch...we have a swa submain to a db...3 more submains to 3 other dbs..one of which goes to a small garageon the se o the flat.
customer says that when he swtches on flouresent lights (any..connected to any of his 4 db's) sometimes his rcd trips..
ive seen this today...
so...ramp test the rcd...(hager 100A 30mA .....fitted it 18 months ago when the last one tripped to early..!) goes off at 17mA every time.
when I switch off the submain to garage .... it goes out at 23ma..and all is fine.
sub main tests fine...
submain db tests fine..all its cabling tests fine....
turn off submain db circuits one at a time...no difference...still trips at 17mA.......
ill return to the job as I ran out of time.....
ANY THOUGHTS....?? GREATFULY ACCEPTED
can it be just a mass of leaky appliances all contributing...???
let me know..
cheers
vitoboy