nearlynew

I was originally going to have a double oven installed so the electrician installed a dedicated cooker circuit with a cooker control unit, 6mm t&e and 32amp mcb.

The plan has changed and I will be having a single oven instead so I will need to replace the 32 amp mcb with a 16 amp. Is this something I'm allowed to change myself or must I use a fully qualified electrician to do it?

Thanks for any advice
 
To expand on what monkeyelectric just said, most single ovens (which use about 10A) come with a plug. That has a 13A fuse in the it to protect the oven flex, so you only need the 32A MCB to protect the 6mm cable and accessories, (which it does just fine). You will of course have to change the cooker connection unit for a socket, for which I think you need to be registered with a scheme for part P in England and Wales, but someone will correct me if I'm wrong (I'm in Scotland). I am going to open a pandora's box/can of worms etc. on here and point out that you don't legally have to use a fully qualified electrician for anything. You just need to be confident that whoever is doing this is competent. One more thing - I wouldn't encourage you to open the consumer unit unless you are very confident that you know what you are doing inside it - there are live components inside even when the main switch is off!
 
saw this one earlier...decided not to reply to it as the O/P is so obviously a builder looking for free advice...

or some DIY joker wanting to know stuff....

and you all fell for it...

madness.....madness...
 
To expand on what monkeyelectric just said, most single ovens (which use about 10A) come with a plug. That has a 13A fuse in the it to protect the oven flex, so you only need the 32A MCB to protect the 6mm cable and accessories, (which it does just fine). You will of course have to change the cooker connection unit for a socket, for which I think you need to be registered with a scheme for part P in England and Wales, but someone will correct me if I'm wrong (I'm in Scotland). I am going to open a pandora's box/can of worms etc. on here and point out that you don't legally have to use a fully qualified electrician for anything. You just need to be confident that whoever is doing this is competent. One more thing - I wouldn't encourage you to open the consumer unit unless you are very confident that you know what you are doing inside it - there are live components inside even when the main switch is off!
Not the most helpful bit of advice on a VERY public forum, except the last sentence.
 
Many thanks for the replies, they have been very useful. I won't dream of opening the consumer unit.

I'm neither a builder or joker and just wanted to know/check whether it was a simple job I could do myself. The single oven is without a plug and must be hardwired.
 

Reply to 32 amp mcb to 16 amp mcb in the DIY Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
975

Similar threads

Why go to the trouble of adding another cable, which I assume would follow the same route as the other ?. Why not upgrade it. It was to try to...
    • Like
Replies
1
Views
159
I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
434

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top