Should the busbar be fed via an rcbo or not

Well if that's the case, it very much depends on the loads being supplied, and there leakage currents. If were talking about normal PC type loads the 32A rating seems a little on the high side. If your talking about commercial type systems, we need a little more information on those loads... Normally those floor outlets only supply general loads in computer suites, so there shouldn't be any problem supplying them from a RCBO protected circuit. What size cable is supplying these plug-in bus bar strips, are they being supplied via a radial circuit(s) or connect to a Ring circuit??
 
I am Sorry Rich, i thought you were concerned about this set up being protected by an RCBO...lol!!!

Yes, normally any under floor or floor mounted or recessed raised floor outlets should be RCD protected. ....Cleaners, especially those from far off foreign shores have a nasty habit of sploshing soapy water everywhere and at everything...lol!!!!
 
We do quite a lot power track under floating floors out here. Our normal installation uses the 63 amp type using various tap of section. We normally don't use RCBO's to protect the track as source, normally it will be a double pole MCB.

We use a normally fused tap off points, as you can not use the unfused type on a 63amp track, you can on a 32amp one though, but only if the tap off is under 3 mteres. All the Tap off points are pre measured 3 mt 5 mt etc.

We normally fit RCD socket oulets rather than protecting the track, as was said earlier if you get one fault on a tap off it will take out the whole track, which really annoys the client.

Also we have quite a few items such as large inkjet printers, commercial shredders etc on non RCD protection.
 
you couldn't protect the 32amp with 30ma -if you go by the recommendations of max 4 workstations at up to 3.5ma each

the loading is only up a bout 2kw unless the drink is confusing me again



keep protection local as possible anyhwow if you have to rcd IT equipment
 
I remember years ago all underfloor busbar trunking / tap-offs to floor boxes were always fed from MCB's. The main issue related to earth leakage from the old CRT monitors.

With the current regs I would always supply via RCBO as the big problem from a design side of things is users plugging in phone chargers, desk fans and I've seen hair straighteners!
 

Reply to 32a busbar feeding floorboxes in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
252
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
724
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
696

Similar threads

  • Question
Cheers guys, enjoyed reading all the responses. I'm an apprentice and it was a conversation that came up at work between two electricians...
2 3
Replies
43
Views
3K
  • Question
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...
2
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top