OP
Graeme Harrold
If the 2.5 supplies a fixed load less than the CCC of the cable, then the 32 amp breaker is providing short-circuit protection only (and obv. earth fault). If it can be shown by calculation that this breaker will operate under short circuit conditions in a time sufficient that the conductors will not rise above their final limiting temperature (from their normal operating temp.) then the circuit complies with BS 7671 and is safe.
EH NO.......The current rating of the MCB CAN NOT BE HIGHER than that of the cable. Absolutely nothing to do with the connected load on this one. The MCB is there to protect the cable not what is connected to it.