Technical arguments aside (and some swerves around the reqs of BS7909 as well) there’s a disconnection between where this post has described it’s start and where it’s at now…. A pub gig is very rarely a toured 2/3 way crossover with processing and 63/1 scenario - so which, exactly, are we providing you advice on?
Powering a 2-3k 4way system initially, perhaps lights/stage also, then expect to use the same distro for 6-12k over the next year or so although not loaded with any stage or lights.
The help I need is just to make sure I'm getting the right parts like making sure the terminal blocks are OK. Just to be pointed in the right direction if I am doing something wrong. Looking at the original Penn Elcom box I now realise it has 2x16a mcbs so even though it has 20a powercon (even if not neutrik) they will never actually receive 20a which I didn't notice when I started reading the thread.
I wire the 32amp ceeform input with 6mm tri into three of the following blocks, I will place the 3 blocks along a din rail mounted along the middle of the inside of the box. These are the only 32amp blocks I can find that will take 2mm-6mm wire and rated at 32a.
Then from the blocks 4mm tri to the neutrik 20a sockets through MCB. They will be crimped using:
and I will use neutrik faston 4.8mm connectors rather than 4.8mm spades as they may only be rated for 15a and I know the neutriks are 20a. I will then heatsink the faston and use the SCDR sleeves
Each socket will have it's own MCB. I have added a 13amp socket I plan to keep a circuit tester in or for charging phone/laptop/convenience.
Of the 12 terminals:
1. 6mm (32a ceeform in) RCBO 32amp type c (The induction loop from the 100a ammeter will measure current on this wire)
2. 4mm (16a ceeform out) RCBO 16amp type c (20a Ammeter installed inline (relies on 16a rcbo protection)
3. 4mm (20a powercon 1) MCB 20amp type c
4. 4mm (20a powercon 2) MCB 20amp type c
5. 4mm (20a powercon 3) MCB 20amp type c
6. 4mm (20a powercon 4) MCB 20amp type c
7. 4mm (20a powercon 5) MCB 20amp type c
8. 4mm (20a powercon 6) MCB 20amp type c
9. 4mm (20a powercon 7) MCB 10amp type b
10. 4mm (20a powercon 8) MCB 10amp type b
11. 4mm (13a socket) MCB 13amp type b
12. 2.5-4mm (100a ammeter rated up to 20a) protected by MCB 6amp type b
Everything here is pretty much perfect for my needs, the only thing I think might need changing is the 9. and 10. My processor is fused at the back and I have wired a blue neutrik socket into the back of it on a patch panel. Which means it could be patched into a 20a supply although the 10amp sockets are for this, but they are on the distro, not the back of the unit.
Reply to 32amp Single phase rackmount distro in the The Welcome Forum area at ElectriciansForums.net
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...