Hi Got situation with one of these heaters. pretty juicy. It does heating & Water. 3-9kw
http://accl.onwirral.net/Downloads/Heatrae_Amptec_Installation_Guide.pdf
Its going to be wired Y Plan but issue is that its being asked of me to put 10mm cable in. Which i would agree on is suitable
BUT what i suggested is that it could be possible to use 6mm.
The cable run is no more than 4 metres from board. there large boxing for cable to lay in. no insulation So by OSG this is fine YES NO?
I mean the cable can take what 46/47 Amps Clipped Direct the max load of the unit would be 37.5 amps.
I recent saw the post on showers with this in mind but thought this could be a different beast as it could be on for long periods of time at max power. So issue is Would a large plastered board boxing in count as Ref B or Ref C. If C then surly 10 amps head room is ample.
I know would be easy to put a 10mm in and be done with it. but there a new 6mm in there already for the original spec asked for. So way i see it is money is money and if we can save SAFELY then why not.
http://accl.onwirral.net/Downloads/Heatrae_Amptec_Installation_Guide.pdf
Its going to be wired Y Plan but issue is that its being asked of me to put 10mm cable in. Which i would agree on is suitable
BUT what i suggested is that it could be possible to use 6mm.
The cable run is no more than 4 metres from board. there large boxing for cable to lay in. no insulation So by OSG this is fine YES NO?
I mean the cable can take what 46/47 Amps Clipped Direct the max load of the unit would be 37.5 amps.
I recent saw the post on showers with this in mind but thought this could be a different beast as it could be on for long periods of time at max power. So issue is Would a large plastered board boxing in count as Ref B or Ref C. If C then surly 10 amps head room is ample.
I know would be easy to put a 10mm in and be done with it. but there a new 6mm in there already for the original spec asked for. So way i see it is money is money and if we can save SAFELY then why not.