Been reading quite a lot of posts but many relevant ones were outdated so thought I'd ask fresh.
Putting in a 3kw single oven (states 13A plug on it), could this be fed from a fused spur off the ring? Theoretically in this case as the board is pretty close by and I'll probably put it on its own circuit anyway. I know I could put 6mm in which would allow for someone to put a huge oven in in the future but as this is my own house and the oven is in a tower with no way of fitting a bigger one, am I fine calculating a smaller sized cable?
3kw cooker + 1kw microwave = 4kw/230 = 17.4A worst case.
Cable run if new circuit would be about 6 metres and clipped direct in the garage, so how about a length of 2.5mm and a 20A breaker?
It seems as though coming off the ring would be fine but with dishwasher, hood etc going it might get a bit close to 32A if someone boils the kettle. Also I think fixed appliances over 2kw should have their own circuit shouldn't they?
Thanks
Putting in a 3kw single oven (states 13A plug on it), could this be fed from a fused spur off the ring? Theoretically in this case as the board is pretty close by and I'll probably put it on its own circuit anyway. I know I could put 6mm in which would allow for someone to put a huge oven in in the future but as this is my own house and the oven is in a tower with no way of fitting a bigger one, am I fine calculating a smaller sized cable?
3kw cooker + 1kw microwave = 4kw/230 = 17.4A worst case.
Cable run if new circuit would be about 6 metres and clipped direct in the garage, so how about a length of 2.5mm and a 20A breaker?
It seems as though coming off the ring would be fine but with dishwasher, hood etc going it might get a bit close to 32A if someone boils the kettle. Also I think fixed appliances over 2kw should have their own circuit shouldn't they?
Thanks