Hi, I’ve been asked to install 5x 3kw ceiling heaters in a room for a salon.
I just want to check how you would install them?
I’m thinking a radial in 4mm2 cable (singles in conduit), from cu to thermostat, to contactor to heaters, 13amp f/spur at each heater?
Customer wants them all to come on at same time hence the contactor.

Advice/ thoughts Welcomed.

Cheers

Wardy
 
Hi - I would confirm manufacturer’s fusing requirements.
Just a reminder that no diversity is allowed so 3000/240 = 12.5A times 5 rads gives a load current of 62.5A.
 
Hi, I’ve been asked to install 5x 3kw ceiling heaters in a room for a salon.
I just want to check how you would install them?
I’m thinking a radial in 4mm2 cable (singles in conduit), from cu to thermostat, to contactor to heaters, 13amp f/spur at each heater?
Customer wants them all to come on at same time hence the contactor.
oughts Welcomed.

Cheers

Wardy
It is recommended that loads of 2KW and above are wired to their own circuit, I would wire 5 Ras/dials 1 for each heater 3 KW is about 13 Amps, 5 3KW is 15000/230 is about 65 A done any cable calcs?
 
a couple of things worth considering

contactors can be noisy, the clunk of a good sized contactor every few minutes might annoy people if it is located in the wrong place.
if it can’t be located where it can’t be heard, a solid state relay could be used instead (silent in operation )

15kw sounds like a lot for 4mm to carry 65A?
if it is a 3 phase supply that could work but if it is single phase I would think splitting the heaters into 3 separate breakers would help to keep your cable size down.

sizing of the contactor is important, don’t go for one that is close to the current intended.
oversize by at least 50% or it will not last the test of time.

on the control circuit side of things, have you considered the lighting circuit?

if you power the stat and contactor coil from the main lights or a neon switch next to the light switch then it is much less likely to be left on by mistake overnight.
it will of course come on automatically whenever the premises are occupied.
 
Thanks for the advice and thoughts guys.
I’m thinking to go with 5x radials.
There is a new dB going in at some point soon so capacity is good.
I will look at location of solenoid/ control box as the majority is open plan so noise of a clunk would be an issue.
Cheers
Much appreciated ?
 
do the heaters have integral thermostats? if so ditch your planned stat. then the contactor only activates when they first switch on in the morning.
 
Why do they want a kill switch to turn them all on/off at once.
Can't they each just be fed via a switched fused spur with neon indicator so at the start/end of the day someone can simply go round and turn them on/off.
 
Why do they want a kill switch to turn them all on/off at once.
Can't they each just be fed via a switched fused spur with neon indicator so at the start/end of the day someone can simply go round and turn them on/off.
idleness.
 
I've been sent to do a similar task involving 4x heaters on one phase. The MCB is 45A and I've been told to wire it via a contactor and a thermostat. Is it right that I can take the power from the supply side of the contactor, to the stat and then from the stat to energize the coil? I am slightly concerned about taking a much smaller cable to the stat as its on a 45A MCB but the chap I'm working with says its fine as there is practically no load on the stat/coil. Is this correct?
 
I've been sent to do a similar task involving 4x heaters on one phase. The MCB is 45A and I've been told to wire it via a contactor and a thermostat. Is it right that I can take the power from the supply side of the contactor, to the stat and then from the stat to energize the coil? I am slightly concerned about taking a much smaller cable to the stat as its on a 45A MCB but the chap I'm working with says its fine as there is practically no load on the stat/coil. Is this correct?
Take the control circuit through a slide lock fuse within the contactor housing, been done that way since Jesus played in goal for Bethlehem
 

Reply to 3kw heaters installation in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
841

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top