Afternoon chaps,

I've got a mate with a rather 2nd hand 3ph compressor he would like me to connect.

I don't do a great deal of commercial work as many of you who know me will know but I want to help him out and gain some experience along the way.

There's an old 3ph panel in his garage with 3x 32a bs3036 which Currently supplies a 3ph+n+e socket outlet in 4mm swa via a 20a 3ph mcb in its own housing.
The compressor has a 5.5kw motor.
I'm happy enough with Sph contactors but haven't a scoobys how this one needs to be connected to allow safe operation.

Can one of you friendly industrial chaps throw some light on it. (pic attached)
any info (or light) muchos appreciated.
Apart from the 6 obvious terminals I'm at a loss.

I await the flames!

cheers [ElectriciansForums.net] 3ph contactor
 
Last edited by a moderator:
Where abouts in Notts are you?

If you can pick me up I’ll show you how to do it.
Sorry but I can’t drive now.

Charge will be 2 pints of good bitter J
 
Last edited by a moderator:
That's a very generous offer by Tony... cheap at half the price! :p

First off... your 5.5kw motor will have an FLA rating of at least 10amps so that contactor and overload should be checked to ensure the overload can be set to the FLA. (It appears to be a 32A o/l but what's the lowest rating on the dial?)

Second... is the contactor coil voltage 240v or 415v (or other)?

And lastly... is the start stop on the front of the DOL housing, or are they remote? Where does that cable go?

.
 
Last edited by a moderator:
No idea what voltage the coil is, I was hoping someone would have seen this particular chappie before.
I'm thinking a pm to tony may be the answer!!
 
No idea what voltage the coil is, I was hoping someone would have seen this particular chappie before.
I'm thinking a pm to tony may be the answer!!

Well, i don't think you'll find anyone better here, when it comes to motor controls Benny. Think yourself dammed lucky he's there on your doorstep too ..lol!!!
 
No plastering or making good, can’t beat it! I’m an artist with a jackhammer.
My last ten years were spent mainly on PLC control systems, great fun with the lunatic boss I had. I loved his reaction when we damaged a £.2M bit of kit “Oh well, sh*t happens”.

It’s each to his own J
 
I learnt about domestic ring mains, cantabrian9. But never having any need of them I’ve never kept up to date with them. We all have our fields, the lads on this site can run rings around me when it comes to regulations regarding domestic installations.

We’re here to help each other!
 
How did you go on with this ?
Ha, Well I went down the other day and the contactor was knackered. But he said "Don't worry, I was wired straight into that thing anyway" (pointing at the pressure switch).

I told him I wouldn't wire it up without OLP for the motor and he didn't want to pay for a new contactor, so I've left him with it!
No doubt he'll be cremating himself as we speak.

Thanks for your input Tony anyhow.
 
thats what i like about us all we are all willing to help and thats a genuine chap and two pints only you old softy!!!
any way another quick check is the actual wiring to to contactor if there is no neutral arouind then assume 230 usully around there on side or look at top the answer is there for stitching
but your problem is solved and you will learn something valuable
 

Reply to 3ph contactor in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

  • Question
Absolutely, yes. It was just a bit of a joke, looking at your quoted Z values. edit. Oh, joking too!.....I see your attempted smile didn't work ...
2
Replies
28
Views
6K
  • Question
Arrgh I see. Didn't note the quotation marks :-(
Replies
13
Views
2K
C
  • Question
I'm not replacing the CU at the house & it's a Protek one, so hope there's some room...Use Crabtree all the time so that's good to know about the...
Replies
42
Views
5K
claret73
C
T
on the original wylex it wasn't, but it is on the crabtree :) Sent from my GT-I9300 using Tapatalk 2
Replies
12
Views
3K
Tidy Max
T
T
Would be very grateful! No, its private network so additional council requirements shouldnt be a problem.... was looking for something to show a...
Replies
16
Views
8K
Trulyshocking
T

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks