Hi. Just having a moment and doubting some work that I have done. Although discussed with a couple of other sparks and niceic tech line and they said was the right way.
House had a single phase board and a 3phase for old storage heaters. Storage heaters out and replaced for lower cost haverlands. Total load less than 50amps. Have replaced both boards for 2 single phase board running from just 2 of the phases ( have put a central 4pole isolator ) upgraded neutral from the isolator to 35mm then 25mm to each board but used existing dno tails from the meter (25mm)
Can anybody see any wrong doing in this?
Be gentle if I have made a cock up but just sat here doubting things!!
House had a single phase board and a 3phase for old storage heaters. Storage heaters out and replaced for lower cost haverlands. Total load less than 50amps. Have replaced both boards for 2 single phase board running from just 2 of the phases ( have put a central 4pole isolator ) upgraded neutral from the isolator to 35mm then 25mm to each board but used existing dno tails from the meter (25mm)