Hi there, heres hoping i can borrow some of your time to corroborate an nic inspector's advice.

The job is to move a 3p+n supply 30m to an adjoining building through a duct in the ground. The customer needs over 70A per phase for his equipment. So coming from the existing kiosk with 3phase cutout with suppliers isolator, the nic inspector has asked for an mcb to be fitted in the kiosk, along with the existing isolator.

So this means fitting a 100A mcb and keeping the 100A isolator? is this correct, surely a 3pole switch fuse would be better?

Any ideas?, thanks.
 
Re: 3phase move

He might be advising installing a 100A MCB to provide discrimination between the circuits overcurrent protection and the supply fuses.

ie. A BS 1361 100A fuse takes 5 seconds to disconnect with a fault current of 630A where a BS 60898 100A B type MCB will disconnect in 0.1 seconds with a fault current of 500A.

Hope this helps.
 
Only a guess, is the equipment down stream protected by MCB`s? if so, fitting fuses upstream could possibly screw your discrimination and tripping times. (Fuse and MCB combinations are the worst).
Maybe thats why the NIC chap suggested MCB`s :confused:
 

Reply to 3phase supply in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

  • Question
Thanks for that advice. I don't know the MV capacity locally, though there are lots of wind farms several miles away so generation is not such a...
Replies
2
Views
900
  • Question
I'm not 100% sure of land ownership of the field with the pole in - I'll check. I appreciate the replies - thanks everyone.
Replies
4
Views
1K
R-Fur has contacted me to post the following for him as he doesn't have access to post in the DIY section..... The DNO are required to maintain...
Replies
6
Views
4K
  • Question
Build by the three little pigs and a wolf banging.in The electrics.
Replies
23
Views
4K
  • Question
This lesser known technique can be used for RCBO protected circuits, allowing a high current test to be used. It's a good one to have in the bag...
Replies
13
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks