- Joined
- Aug 11, 2007
- Messages
- 169
- Reaction score
- 52
Could some one offer some advice please. I have been asked to look at a farm supply that has just started tripping out. 100 A per, 3 phase supply, + nutral, TNCS, + an earth spike. Client said that when EDF moved the supply from overhead to underground in SWA they suggested putting in the rod as backup. Ze 0.34
without spike
The supply feeds through meter into 4 pole RCD 80A 30mA. The whole farm is then split from this into varoius buildings. The problem is that one unit constructed from portacabins appears to produce an intermittant earth leakage of around 16 - 20mA. I have tested all circuits and they test out fine.
The causes of the tripping is the switching of any circuit within this unit.
I have had a similar problem in a domestic situation when next doors electric strimmer tripped the house
RCD. This was sorted by fitting a time delay RCD in its place.
Question: 1) Can you get 4 pole time delay RCDs ?
2) Can the RCD become more and more sensitive for some reason ? it does test out ok when all
other circuits are removed.
3) Is 5.4mA earth leakage acceptable for a flourescent fitting, all 4 of them produce around 14mA
4) I can't get a Zs from the DB supplying the unit as the RCD drops out, should I dissconnect all
Power to the farm and do an R1+R2 on the cable ?
Many thanks for all help, Pat
without spike
The supply feeds through meter into 4 pole RCD 80A 30mA. The whole farm is then split from this into varoius buildings. The problem is that one unit constructed from portacabins appears to produce an intermittant earth leakage of around 16 - 20mA. I have tested all circuits and they test out fine.
The causes of the tripping is the switching of any circuit within this unit.
I have had a similar problem in a domestic situation when next doors electric strimmer tripped the house
RCD. This was sorted by fitting a time delay RCD in its place.
Question: 1) Can you get 4 pole time delay RCDs ?
2) Can the RCD become more and more sensitive for some reason ? it does test out ok when all
other circuits are removed.
3) Is 5.4mA earth leakage acceptable for a flourescent fitting, all 4 of them produce around 14mA
4) I can't get a Zs from the DB supplying the unit as the RCD drops out, should I dissconnect all
Power to the farm and do an R1+R2 on the cable ?
Many thanks for all help, Pat