dkpramanik

For a LT panel which have two incoming 5000A ACB from 3phase, 3MVA Dyn transformer & 630A ACB from 3 phase, 250kW Black Start DG set and have several outgoing 3 phase, 100A-300A MCCB for remote distribution panel and have some single phase load.

Could anyone pls advise which type of 3 Pole or 4 Pole ACB and MCCB should I use for the LT panel as per IEC standard?

What are the advantage and disadvantage of using 4 pole vs 3 pole?
 
Last edited by a moderator:
Apart from anything else, nothing in your OP makes much sense!! lol!! Rule of thumb incomers and any stand-by Generator incomer on to a switchboard, should always be 4 pole as well as any bus couplers.... that's as far as i'm going on this one!! lol!!
 
I'm glad you said that Tony, I was gonna say it looked like a homework question, and a poorly worded one at that?! But I decided to cancel before I posted, the OP is in Bangladesh, I didn't think there was such a thing as an Indian electrical qualification? lol, or is that just me being really ill informed? A mate of mine was working out there and he seemed to think that there wasn't even a code of practice for wiring in India???
 
I'm glad you said that Tony, I was gonna say it looked like a homework question, and a poorly worded one at that?! But I decided to cancel before I posted, the OP is in Bangladesh, I didn't think there was such a thing as an Indian electrical qualification? lol, or is that just me being really ill informed? A mate of mine was working out there and he seemed to think that there wasn't even a code of practice for wiring in India???

Bangladesh is a country - it is not in India. Perhaps you are thinking of Bangalore? Lol
 
My question is simple-

For that LT panel- I have selected 4 pole ACB and MCCB, I need technical clarification of selecting such type of CB

so my question no 1- what are the advantages of using 4 pole CB rather than 3 pole CB?

and question no 2- if I select 3 pole- what are the disadvantages of 3 pole CB rather than 4 pole CB..
 

Reply to 4 pole vs 3 pole switches/breaker in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Thanks, thats what I assumed , many different manufactures make similar models to mine, again unmarked. As to the photo I will need to join...
Replies
2
Views
990
  • Question
We use one from Stephill generators, it covers the while check / switch / return sequence and included a charger to keep the generator's battery...
Replies
3
Views
1K
I have figured it out, ordered 4 pole impulse relays from Siemens - 16 amp. Hope it will be as good as thought. Often reality does not equal...
Replies
9
Views
1K
  • Question
Scott to start with usually when you see a white and black it’s normally a switch. I get upset when electrical people don’t wrap the white wire...
Replies
2
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks