Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss 40 Amp single pole n/c main contractor? in the UK Electrical Forum area at ElectriciansForums.net
Would you mind explaining what you need it for? ThanksI need a 40A single pole contactor. The main contacts to be normally closed in the distant passed I seem to remember you could get them.
Anyone know where to get them?
Thanks in advance
I have a client that wants to install 3 showers, the supply Is limited to 63Amp so I am looking into automating it so as only 1 shower can be used at a time. Current detection will be needed down stream hence the N/C line contacts.Would you mind explaining what you need it for? Thanks
Reply to 40 Amp single pole n/c main contractor? in the UK Electrical Forum area at ElectriciansForums.net